The EnergyPlus datasets are primarily based on ASHRAE Handbook data which gives 
very little guidance regarding thermal emissivity and solar absorpance.  In the 
datasets, the thermal emissivity is 0.9 for all materials.  Beware of using 
values for "new" galvanized steel.  Things weather and get dirty, so the new 
value does not apply for the long term.  

The Florida Solar Energy Center (FSEC) has published several reports regarding 
roof properties and their effect on cooling loads.  A list of publications may 
be found at:

http://www.fsec.ucf.edu/bldg/resources/publications/index.htm

Two especially pertinent reports are:

http://www.fsec.ucf.edu/bldg/pubs/cr670/index.htm - Lots of measured property 
data  

http://www.fsec.ucf.edu/bldg/pubs/cr1336/cr1336.htm - Table 1 lists solar 
reflectances for six new and weathered materials  


Ned and Agas, would you please send me citations for the sources you are using 
for property data?

Mike




On 4 May 2004, at 15:13, Edward Lyon wrote:

> I have previously noted that there are lot of "differences" between
> properties in material libraries and available reference data.  Most
> often I find that insulation values are not adjusted for thermal
> bridging elements.  I would check manufacturer data for specific
> products.  There is also an LBL web site with tested values for
> different types of roofing materials.  You are on the right track,
> always question the reasonableness of the library data....
> 
> Ned Lyon
> 
> Senior Project Manager
> Simpson Gumpertz & Heger Inc.
> 
> 41 Seyon Street
> Building #1, Suite 500
> Waltham, MA  02453
> 
> Phone:  781-907-9000
> Fax:  781-907-9009
> 
> 
> >>> agas@xxxxxxx 5/3/2004 10:41:06 AM >>>
> Could someone clear up the different thermal properties of roof 
> sheets.
> I have data from a McGraw-Hill book with a chart indicating the 
> following for new galvanised sheet:
> 
> Solar reflectance 0.35
> Solar absorbtance (inverse of refl.) 0.65
> Far IR emissivity 0.15-0.23
> Far IR reflectance (inverse of emissivity) 0.77--.85
> 
> BLASTMaterials.IDF (included in E+ DataSets directory) has the 
> following:
> 
> MATERIAL:Regular,METAL - GALVANIZED STEEL 1 / 16 IN,  !- Material 
> Name
> Smooth,  !- Roughness
>   1.6000000E-03,  !- Thickness {m}
>    45.31000    ,   !- Conductivity {w/m-K}
>    7833.020    ,   !- Density {kg/m3}
>    500.0000    ,   !- Specific Heat {J/kg-K}
>   0.9000000    ,   !- Thermal Emittance
>   0.2300000    ,   !- Solar Absorptance
>   0.2300000    ;   !- Visible Absorptance
> 
> This seems to be quite different. What are the correct figures to use?
> 
> What are the relevant figures for different coloured painted steel 
> corrugated roof sheets, e.g. white, light green ?
> 
> regards,
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov 
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/ 
> 
> Attachments are not allowed -- please post any files to the appropriate
> folder in the Files area of the Support Web Site.
> 
> 
> 
> Yahoo! Groups SponsorADVERTISEMENT
> var lrec_target="_top";var lrec_URL = new Array();lrec_URL[1] =
> "http://rd.yahoo.com/SIG=129sdta1m/M=295196.4901138.6050264.3001176/D=groups/S=1
> 705007389:HM/EXP=1083681678/A=1894283/R=0/id=flashurl/SIG=118tuuldn/*http://comp
> anion.yahoo.com/?.cpdl=srch";var link="javascript:LRECopenWindow(1)";var
> lrec_flashfile =
> 'http://us.a1.yimg.com/us.yimg.com/a/ya/yahoo_companion/broom_lrec.swf?clickTAG=
> '+link+'';var lrec_altURL =
> "http://rd.yahoo.com/SIG=129sdta1m/M=295196.4901138.6050264.3001176/D=groups/S=1
> 705007389:HM/EXP=1083681678/A=1894283/R=1/id=altimgurl/SIG=118tuuldn/*http://com
> panion.yahoo.com/?.cpdl=srch";var lrec_altimg =
> "http://us.a1.yimg.com/us.yimg.com/a/ya/yahoo_companion/lrec.gif";var lrec_width
> = 300;var lrec_height = 250; Yahoo! Groups Links To visit your group on the web,
> go to: http://groups.yahoo.com/group/EnergyPlus_Support/ 
>   To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx 
>   Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx



------------------------ Yahoo! Groups Sponsor ---------------------~-->
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
---------------------------------------------------------------------~->

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
     http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
     EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
     http://docs.yahoo.com/info/terms/