Subdividing surfaces can affect convection coefficients with some of the
convection algorithms, and it can affect distribution of solar gains when using
FullInteriorAndExterior solar distribution. I would suggest turning on
reporting of inside and outside convection coefficients and surface
temperatures. If this does not explain the differences, then please upload
your input files to the yahoo group files area or send as a zipped e-mail
attachment to energyplus-support@xxxxxxxx
Mike
On 3 May 2004, at 19:48, vamsi gooje wrote:
>
> Hi,
>
> I have modeled a single zone with no system.
>
> When I'm modeling a wall surface as 3 different panels together instead of just
> one, I get a 1-2 degF higher temperature. I understand that EnergyPlus do not
> take heat transfer between the edges into consideration. If this is true, then
> why is this difference. Please correct me if I'm wrong.
>
> Thank you,
>
> Vamshi
>
>
> ---------------------------------
> Do you Yahoo!?
> Win a $20,000 Career Makeover at Yahoo! HotJobs
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
---------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/