This wall must be modeled as two heat transfer surfaces, one representing the 
portion which separates Zones A and B, and a second surface representing the 
portion which separates Zones A and C.

Mike


On 7 May 2004, at 15:07, jgrenha wrote:

> Consider a wall that is a frontier of one zone in one side, and a 
> frontier of two other different zones on the other side. When you 
> specify the wall you might define the OutsideFaceEnvironment as 
> OtherZoneSurface. In this case you can only define a zone, not both 
> zones, and after running it will give a warning. 
> 
> Yours 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx



------------------------ Yahoo! Groups Sponsor ---------------------~-->
Yahoo! Domains - Claim yours for only $14.70
http://us.click.yahoo.com/Z1wmxD/DREIAA/yQLSAA/dkFolB/TM
---------------------------------------------------------------------~->

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
     http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
     EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
     http://docs.yahoo.com/info/terms/