At 05:58 AM 5/24/2004, mby wrote:
>I constantly obtain the following warning message:
>"Warning World coordinate system selected. Some building zone"
>
>As I do switchable glazing, probably I do need
>daylighting calculations and I may need to get rid of
>this warning.
You won't necessarily need to get rid of the warning. It's telling you
that you selected "world coordinates" in your "SurfaceGeometry" object but
have non-zero origins in the Building and Zone statements. The Detailed
Daylighting model uses these non-zero coordinates as you enter the
reference points for the daylighting in "relative (to building/zone
origins) coordinates". The World Coordinate system does not use the
building/zone origins at all.
Linda
EnergyPlus WebSite: http://www.energyplus.gov
Owner: EnergyPlus_Support list
Member: EnergyPlus Development Team
[Non-text portions of this message have been removed]
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Yahoo! Domains - Claim yours for only $14.70
http://us.click.yahoo.com/Z1wmxD/DREIAA/yQLSAA/dkFolB/TM
---------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/