I have confirmed that there is a problem with the zone list multipliers by
setting the individual zone multipliers to 38 and setting the zone list
multiplier to 1. The answer should be the same as the original case with a
zone list multiplier of 38 and individual zone multipliers of 1, but it is not.
The zone list mutliplier is not being applied to internal gains such as LIGHTS
and ELECTRIC EQUIPMENT. Use the Zone Multiplier field in the ZONE object
instead.
However, this particular file will still not work, because the HVAC equipment
is not autosized. If you look at the reported values for ZONE/SYS AIR TEMP,
you will see that the multiplied zones are not maintaining setpoint. Zone
multipliers multiply the zone loads only and expect the HVAC equipment to be
large enough to meet the multiplied load. So, you need to autosize the HVAC
equipment or specify capacities that are 38 times larger for the multiplied
zones.
Mike
On 23 May 2004, at 20:01, Rahul Chillar wrote:
> Hello Leung
>
> Although i wont be able to address all your questions here are some reasons that
> are affecting the electricity and energy consumption of the 40 story building
> you are simulation.
>
> 1).For floors that are multiplied, connect exterior boundary conditions of the
> floor to the ceiling and vice versa.
>
> 2). Since exterior convection coefficients vary with elevation, locate the
> typical middle floor zones midheight between the lowest and highest middle
> floors to be modeled.
>
> 3).Shading must be identical for all multiplied floors or less accurate results
> may be obtained by using the zone list multiplier.
>
> Hope this helps
>
> Thanks
>
> >>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>
> Rahul Chillar
> >>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>
> Graduate Research Assistant
> Building Systems Laboratory
> Mechanical Engineering Department
> University of Illinois- Urbana Champaign
> >>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>
> Phone: Office 217-2441346
> Mobile 217-7213063
>
> >>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>
>
>
>
> i50330513 <50330513@xxxxxxxxxxx> wrote:
> I make good use of `EnergyPlus' program to predict the energy
> performance of a commercial building which is a 40-story building.
> In fact, I had already simulated the 40-story building.
>
> In order to reduce the amount of input of the identical floors and
> have a shorter computational time, Zone List Multiplier field in the
> Zone Group object are used to multiply from 1st to 38th floors.
> However, after simulation of the building with this Multiplier
> field, I found that the total electricity use (Electricity:Facility)
> and the plant loop cooling demand of the building are much less than
> that of the building without using the field of Zone List
> Multiplier.
>
> Is there any input error in the program? The Zone Group object is
> shown as follows. You can see that the Zone List multiplier is set
> to 38 in the 1st FLOOR. Does it mean that the 1st FLOOR is
> multiplied by 38? If yes, why the total electricity and the cooling
> loads are much less than that of the building without the use of
> Zone List multiplier field.
>
> ---------------------------------------------------------
> ZONE GROUP,
> GF FLOOR, !- Zone Group Name
> GF FLOOR LIST, !- Zone List Name
> 1; !- Zone List Multiplier
>
> ZONE GROUP,
> 1st FLOOR, !- Zone Group Name
> 1st FLOOR LIST, !- Zone List Name
> 38; !- Zone List Multiplier
>
> ZONE GROUP,
> RF FLOOR, !- Zone Group Name
> RF LIST, !- Zone List Name
> 1; !- Zone List Multiplier
> ---------------------------------------------------------
>
> I hope you make some recommendation for me. Thanks for your
> attention.
>
> Leung
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
>
>
>
> ---------------------------------
> Yahoo! Groups Links
>
> To visit your group on the web, go to:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.
>
>
>
> ---------------------------------
> Do you Yahoo!?
> Yahoo! Domains - Claim yours for only $14.70/year
>
> [Non-text portions of this message have been removed]
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
---------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/