Re: [EnergyPlus_Support] Question:About the Mean Air Temperature and Mean Radiant Temperature
What are the setpoints for the zone thermostat and the radiant system? What
are the zone mean air and mean radiant temperatures? My guess is that the air
system is overcooling the zone air by providing the minimum flow rate of cold
air.
Mike
On 31 May 2004, at 10:51, zhen tian wrote:
> Hi, All:
>
> I just try to simulate one single zone with Constant Flow Hydrolic Radaint
> Cooling system and a VAV system to check the simulation result. I set the
> radaint cooling system as the priority 1 and air system as 2. The supply air
> temperature is 13 degree C and air flow rate is autosizing. (The radiant system
> undertakes most cooling load).
>
> The weird thing is that the Mean Radiant Temperature is higher than the Mean Air
> Temperature. If I only use the radiant cooling system, these two temperature are
> very similar. Is this resulted from air system?
>
> How can I control the indoor mean radiant temperature with air system in the
> thermosate setting? Because the manual says zone thermosate controls overall
> operation of componentes while the hydrolic system temperature control type can
> only control the radiant system.
>
> Thanks.
>
> Best regards,
>
> Zhen Tian
>
>
> ---------------------------------
> Do you Yahoo!?
> Friends. Fun. Try the all-new Yahoo! Messenger
>
> [Non-text portions of this message have been removed]
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/