There are at least two ways to approach this:

1) as you say, combine all the windows of the same type on the same wall to 
one of equivalent area.  Studies have shown the results to be very similar 
and the less surfaces will take less computation time.

2) there is a Window Multiplier in the Window/Surface:HeatTransfer:Sub object.
   N2 , \field Multiplier
        \note Used only for Surface Type = WINDOW or GLASSDOOR
        \note Non-integer values will be truncated to integer
        \default 1.0
        \minimum 1.0

You can use this field to easily have the number of windows "multiplied" on 
a wall.

Note that the field in the zone "Solar Distribution" should then be 
"FullExterior" and NOT "FullExteriorandInterior".


Linda

EnergyPlus WebSite: http://www.energyplus.gov
Owner: EnergyPlus_Support list
Member: EnergyPlus Development Team



[Non-text portions of this message have been removed]



------------------------ Yahoo! Groups Sponsor --------------------~--> 
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
     http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
     EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
     http://docs.yahoo.com/info/terms/