This depends on the system type. For DX cooling, this is controlled in the
unitary or furnace equipment object along with a ZONE CONTROL:HUMIDISTAT
object. See the FurnaceWithDXSystemRHcontrol.idf and WindACRHControl.idf
examples.
For chilled water systems, use the SET POINT MANAGER:SINGLE ZONE MAX HUM to
control the setpoint leaving the chilled water coil. See the
5ZoneWaterCooled_HighRHControl.idf example.
Mike
On 12 Jun 2004, at 17:54, yang huiyuan wrote:
> Wheather can I control the Relative Humidity?
>
>
>
> ---------------------------------
> Do You Yahoo!?
> ÏÓÓÊÏä̫С£¿ÑÅ»¢µçÓÊ×ÔÖúÀ©ÈÝ£¡
>
> [Non-text portions of this message have been removed]
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/