There is something wrong with the sizing inputs, because the condenser water 
pump flow rate is being sized to zero.  You should be able to autosize the 
entire condenser loop and all of its components and it will automatically match 
the chiller's condenser water flow rate.  See p. 317 (pdf p. 345) of the Input 
Output reference, Item 4. 

Mike


On 15 Jun 2004, at 18:20, carmen herrero prada wrote:

> Hello all,
> 
> I am having some problems while simulating condenser
> loop water cooled with a cooling tower. I am
> autosizing everything (plant sizing), except the
> Design Water Flow rate (m3/s) which has to be the same
> that appears in the chiller object, in the field:
> Design Condenser Volumetric Flow rate (m3/s)
> 
> But, althouth I have tried with different options (as
> creating a schedule for a Condenser Temperature
> Setpoint node in the Condenser Loop object or just
> typing AIR to use the outdoor air wet-bulb as the
> setpoint, as i have seen in the example files) I keep
> getting the same errors:
> 
> ** Warning ** Check input. Pump nominal power or motor
> efficiency is set to 0, for pump=CONDPUMP
>    ** Warning ** Check input. Pump nominal volumetric
> flow rate is set or calculated = 0, for pump=CONDPUMP
>    ** Severe  ** COOLING TOWER:SINGLE SPEED "TOWER".
> Free convection air flow rate must be less than the
> design air flow rate.
>    ** Severe  ** COOLING TOWER:SINGLE SPEED "TOWER".
> Free convection UA must be less than the design tower
> UA.
>    **  Fatal  ** Errors found in Cooling Tower input
> 
> 
> I do not understand what is going on. I have also
> autosized the condenser pump and I have tried by
> changing the exit temperature and the delta
> temperature in the plant sizing object for the
> condenser plant.
> 
> I am sure i am missing something. Could anybody tell
> me what it is?
> 
> Thanks a lot,
> 
> Carmen.
> 
> 
> 
> ______________________________________________________________________
> Yahoo! lanza su nueva tecnología de búsquedas
> ¿te atreves a comparar?
> http://busquedas.yahoo.es
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx



------------------------ Yahoo! Groups Sponsor --------------------~--> 
Yahoo! Domains - Claim yours for only $14.70
http://us.click.yahoo.com/Z1wmxD/DREIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
     http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
     EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
     http://docs.yahoo.com/info/terms/