Re: [EnergyPlus_Support] Question about "People" object?
EnergyPlus does not limit thermal comfort results to the standard reporting
ranges. If -4 indicates that people are cold, then -9 indicates that they are
very very cold. Report the values for Mean Air Temperature and Mean Radiant
Temperature in the zone. If these values are reasonable, then check the inputs
in the Poeple object.
Mike
On 18 Jun 2004, at 2:27, i50330513 wrote:
> Hello,
>
> I have a question about "People" object.
>
> I want to calculate "predicted mean vote"(PMV) using the Fanger
> thermal comfort model. I expect that the thermal sensation scale is
> between -4 and 4. However, after simulation, I found that the scale
> can be very large, i.e. between -9 to 4. Is it abnormal? Is there
> any input error in the People object?
>
> Thanks for your help.
>
> Leung
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
Yahoo! Domains - Claim yours for only $14.70
http://us.click.yahoo.com/Z1wmxD/DREIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/