Re: [EnergyPlus_Support] Site wind conditions



You can report "Wind Pressure" in [Pa] for each COMIS surface.  There are no 
other wind report variables except the "Wind Speed" from the weather file.

My understanding of the reference heights is that the "Reference Height of the 
Recorded Data" in the section "Comis Simulation", is as you suggest, this value 
is the height of the instrument above the ground independently of the altitude 
of the station.

In the COMIS CP Array object, the "Reference Height for CP Data" value is 
compared to the above height for the recorded data and the local wind speed at 
the building is adjusted accordingly.

Mike


On 24 Jun 2004, at 9:44, abeltablada wrote:

> Hello,
> I have a question about "Comis Site Wind Conditions". Can I
> get, as output, the characteristics of the wind near the building 
> from the calculation of the parameters "Wind Direction, Plan Area 
> Density, Wind Velocity, Profile Exponent and Surrounding Building 
> Height"?
>  I want to compare the values of the wind speed of the weather file 
> with the ones of the site calculated by E+.
> Concerning the "Reference Height of the Recorded Data" in the 
> section "Comis Simulation", Is this value the height of the 
> instrument above the ground independently of the altitude of the 
> station?
> Is the difference of altitude between the station and the site taken 
> into account for the calculation of the "Site wind
> conditions"?
> Thanks for your help,
> Abel.
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx



------------------------ Yahoo! Groups Sponsor --------------------~--> 
Yahoo! Domains - Claim yours for only $14.70
http://us.click.yahoo.com/Z1wmxD/DREIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
     http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
     EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
     http://docs.yahoo.com/info/terms/