[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
RE: [EnergyPlus_Support] cooling load
Hello
Brents email gives a good explaination for the different loads in the zone.
also i would like to say that adding the insulation would be Decreasing the TOTAL Cooling Load on the Building , but the effect would only be showing on the ground floor due to no insulation barrier on the ground floor ceiling and it being able to release the heat to the upper floor.
If you do a Total SUm of COoling Loads for the entire building before and After insulation i think it will be less after adding insulation.
Thanks
Rahul Chillar
Graduate Research Assistant
Building Systems laboratory
University of Illinois U C.
"Griffith, Brent" <brent_griffith@xxxxxxxx> wrote:
I bet that the ground floor slab is acting like a source of cooling in an otherwise free floating building. Check that the ground temperatures are reasonable. If you want better ground temperature values, you could run slab.exe with the interior temperatures found in the first simulation.
-----Original Message-----
From: zhen tian [mailto:tianzhen9@xxxxxxxxx]
Sent: Wednesday, July 07, 2004 10:04 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: RE: [EnergyPlus_Support] cooling load
Hi, Rahul:
I underatnd the cooling load in the upper floor will increase with added insulation because the insulation will be the barrier which prevents the heat going out.
But I can not understand why the cooling load in the groud floor goes down with added insulation in the upper floor roof.
Thank you.
Zhen
Rahul Chillar <chillarrahul@xxxxxxxxx> wrote:
Tek
this is what is happening.
Outside temperature is higher than inside, your insulation provides a barrier for heat to go from outside to inside, this makes perfect sense.
Now the building heats up all day in sun , its temperature rises.
The building is hot enougth and now needs to dissipate heat , The insulation Blocks the heat from going out. This makes sense too.
Now what is happening is ,that when the building is trying to cool Or lets talk each floor is trying to cool>>
Ground Floor is trying to Cool: It dissipates the heat to ground floor ceiling which then goes into the upper floor zone. So upper floor gets heat from lower floor and this lower floor ceiling is obviously not insulated so there is nothing to block the heat being dissipated from ground to upper floor.
Now
Upper Floor is trying to cool: It has heat from lower floor + its own heat which it tries to dissipate and now there is insulation on the upper floor ceiling (your roof) , THIS insulation will block the heat going out from upper floor , so there will be an increase in the COOLING LOAD for upper floor.
What you need to do is to vary the insulation parameters and find an optimum which can get you the lowest cooling load .
This is the a wonderful capability of the E+ to vary the parameter and see the effects which you should try.
I have neglected the heat dissipation from the walls of the building , cause they are unaffected.
Window heat gain depends a lot on the window area compared to wall area , You may get more heat gain from window than the system cooling load requirment , because your walls will also radiate heat , convect heat to the enviornment outside. It is dependent quite a bit on outside enviornment conditions which you need to look at when this happens. Which hour / what is the temperature outside , wind speed etc.
Also just make sure you are comparing the same units for loads (and not comparing rate Watt vs Load Joule) thought i am sure you might have taken care of that.
Hope this helps
Thanks
Rahul Chillar
Graduate Research Assistant
Building Systems laboratory
University of Illinois U C.
Univerity of
teklay Weldeabzgi <teklay1979@xxxxxxxxx> wrote:
Rahul and Rohini you are right it may be the case.
but what i am confusing is, my building is a two story
(G+1) office building. when i see the results of the
simulation with and without insulation on the roof of
the upper floor of the building. the cooling load on
the ground zones decrease with insulation but for the
upper floor zones the cooling load increase with
insulation which seems an error.
another problem is on the window heat gain. does the
window heat gain directly sum up to the cooling load ?
if so in my report the window heat gain is greater
than the cooling load, why is this happens ?
--- Rahul Chillar <chillarrahul@xxxxxxxxx> wrote:
> Tek
> Since the building you are modelling is in a hot
> climate (equator) and there are no heating loads ,
> only airconditioning through out the year , The
> insulation would have negative effect. Infact your
> building would be heating up all day and will not be
> able to lose the heat due to insulation. This
> approach is suitable for cold climates. The
> explaination given by Rohini in email earlier
> justifies it well.
>
>
> Thanks
>
> Rahul Chillar
>
> Grad Research Assistant
>
> Building Systems Lab
>
> University of Illinois UC
>
>
>
> Rohini Brahme <rbrahme@xxxxxxxx> wrote:
> The reason could be that the heat from inside the
> building now has more difficulty in going out by
> conduction. This usually happens in office buildings
> which are dominated by internal loads and solar
> loads through windows. One way to check if this is
> true is to compare the internal temperatures without
> the system in the two cases. My guess is that the
> internal temperatures would be higher with
> insulation, and that these temperatures are higher
> than outside temperature on average. If you have
> enough air exchange with the outside (either by
> infiltration, or natural ventilation) then these
> numbers will be closer to the outside temperature.
> Also, make sure that the heating load is decreasing.
>
>
>
> Rohini
>
> -----Original Message-----
> From: teklay Weldeabzgi
> [mailto:teklay1979@xxxxxxxxx]
> Sent: Mon 7/5/2004 6:16 AM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Cc:
> Subject: [EnergyPlus_Support] cooling load
>
>
>
> when i simulate a ground plus one office
> building i
> gokt some confusing result due to insulation
> in the
> roofs. the roof in the upper floor is
> corregated iron
> sheet and a chip wood ceiling with an air
> space b/n
> them. when i see the annual cooling load for
> this base
> case and inserting an insulation just below
> the iron
> sheet the cooling load with insulation is
> greater than
> the cooling load with out insulation. but i
> doubt this
> result is correct b/c using insulation is to
> reduce
> the cooling load, but in my case it increases.
> can any one what will the possible reason. i
> have
> checked my idf file but i can't find any
> error.
>
> thanks
> tek
>
>
>
> __________________________________
> Do you Yahoo!?
> Yahoo! Mail - Helps protect you from nasty
> viruses.
> http://promotions.yahoo.com/new_mail
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
>
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any
> files to the appropriate folder in the Files area of
> the Support Web Site.
>
>
>
>
> Yahoo! Groups Sponsor
> ADVERTISEMENT
> click here
>
< http://us.ard.yahoo.com/SIG=129ahl4h4/M=295196.4901138.6071305.3001176/D=groups/S=1705007389:HM/EXP=1089112586/A=2128215/R=0/SIG=10se96mf6/*http://companion.yahoo.com>
>
>
< http://us.adserver.yahoo.com/l?M=295196.4901138.6071305.3001176/D=groups/S=:HM/A=2128215/rand=894073014>
>
>
>
> _____
>
> Yahoo! Groups Links
>
>
> * To visit your group on the web, go to:
>
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> * To unsubscribe from this group, send an
> email to:
>
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
<mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>
>
>
> * Your use of Yahoo! Groups is subject to
> the Yahoo! Terms of Service
> < http://docs.yahoo.com/info/terms/> .
>
>
>
>
> [Non-text portions of this message have been
> removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files
> to the appropriate folder in the Files area of the
> Support Web Site.
>
>
>
> Yahoo! Groups SponsorADVERTISEMENT
>
>
> ---------------------------------
> Yahoo! Groups Links
>
> To visit your group on the web, go to:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> Your use of Yahoo! Groups is subject to the
> Yahoo! Terms of Service.
>
>
>
> Thanks
> Rahul Chillar
> Grad Student
> Building Systems lab
> Univ Of Illinois Urbana Champaign
>
>
> ---------------------------------
> Do you Yahoo!?
> New and Improved Yahoo! Mail - Send 10MB messages!
>
> [Non-text portions of this message have been
> removed]
>
>
>
> ------------------------ Yahoo! Groups Sponsor
> --------------------~-->
> Make a clean sweep of pop-up ads. Yahoo! Companion
> Toolbar.
> Now with Pop-Up Blocker. Get it for free!
>
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
>
--------------------------------------------------------------------~->
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
>
=== message truncated ===
__________________________________
Do you Yahoo!?
Yahoo! Mail - 50x more storage than other providers!
http://promotions.yahoo.com/new_mail
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups SponsorADVERTISEMENT
---------------------------------
Yahoo! Groups Links
To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.
Thanks
Rahul Chillar
Grad Student
Building Systems lab
Univ Of Illinois Urbana Champaign
---------------------------------
Do you Yahoo!?
Yahoo! Mail - 50x more storage than other providers!
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups SponsorADVERTISEMENT
---------------------------------
Yahoo! Groups Links
To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.
---------------------------------
Do you Yahoo!?
Yahoo! Mail - 50x more storage than other providers!
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Sponsor
ADVERTISEMENT
<http://us.ard.yahoo.com/SIG=12951g932/M=295196.4901138.6071305.3001176/D=groups/S=1705007389:HM/EXP=1089302646/A=2128215/R=0/SIG=10se96mf6/*http://companion.yahoo.com> click here
<http://us.adserver.yahoo.com/l?M=295196.4901138.6071305.3001176/D=groups/S=:HM/A=2128215/rand=185699122>
_____
Yahoo! Groups Links
* To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
* To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>
* Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service <http://docs.yahoo.com/info/terms/> .
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups SponsorADVERTISEMENT
---------------------------------
Yahoo! Groups Links
To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.
Thanks
Rahul Chillar
Grad Student
Building Systems lab
Univ Of Illinois Urbana Champaign
---------------------------------
Do you Yahoo!?
New and Improved Yahoo! Mail - Send 10MB messages!
[Non-text portions of this message have been removed]
------------------------ Yahoo! Groups Sponsor --------------------~-->
Yahoo! Domains - Claim yours for only $14.70
http://us.click.yahoo.com/Z1wmxD/DREIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/