RE: [EnergyPlus_Support] Re: Material Properties



yes
this explanation makes  the implementation a lot simpler and easier.

Thanks
Rahul Chillar


At 05:29 PM 7/19/2004 +0200, you wrote:
>R = thickness / Thermal conductivity
>Then if you know thermal conductivity you can "calculate" R or vice versa.
>
>
>JOSEP SOLE
>Dirección Tecnica POLIGLAS
>nueva dirección mail : josep.sole@xxxxxxxxxxx
>
>-----Mensaje original-----
>De: chillarrahul [mailto:chillar@xxxxxxxx]
>Enviado el: lunes, 19 de julio de 2004 16:55
>Para: EnergyPlus_Support@xxxxxxxxxxxxxxx
>Asunto: [EnergyPlus_Support] Re: Material Properties
>
>
>Hello
>
>In this case i can suggest 3 options:
>
>First you can break your 4 inch insulation into two insulation layers
>of 1 inch and 3 inch and specify the properties from the dataset  ,
>or something like that  and proceed ahead.
>Second is that you can look up the properties in some material
>handbook and just replace the required fields.
>Third is if you simply have the R value of the material ,(use the
>Material-R  field, in this case you wont require the thickness of the
>material)
>
>Hope this helps
>
>Thanks
>Rahul  Chillar
>Grad Research Assistant, Building Systems Lab
>Mechanical Engineering , University of Illinois - UC
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "khizir_mahmud"
><khizir_mahmud@y...> wrote:
> > Hi
> >
> > Thanks for the guideline of finding the values of the building
> > material properties . Now I am working with the following materials
> >
> > 1. 0.5 mm galv. steel sheet
> > 2. Insulated Polyurethane (3 in)
> > 3. Insulated Polyurethane (4 in)
> >
> > From the BLASTMaterials.idf file i got the following properties ,
> >
> > 1. MATERIAL:Regular,METAL - GALVANIZED STEEL 1 / 16 IN,  !-
>Material
> > Name
> >  Smooth,  !- Roughness
> >   1.6000000E-03,  !- Thickness {m}
> >    45.31000    ,   !- Conductivity {w/m-K}
> >    7833.020    ,   !- Density {kg/m3}
> >    500.0000    ,   !- Specific Heat {J/kg-K}
> >   0.9000000    ,   !- Thermal Emittance
> >   0.2300000    ,   !- Solar Absorptance
> >   0.2300000    ;   !- Visible Absorptance
> >
> > 2.  MATERIAL:Regular,INS - EXPANDED POLYURETHANE R11 3 IN,  !-
> > Material Name
> >  VeryRough,  !- Roughness
> >   7.0000000E-02,  !- Thickness {m}
> >   2.0000000E-02,   !- Conductivity {w/m-K}
> >    32.03000    ,   !- Density {kg/m3}
> >    1580.000    ,   !- Specific Heat {J/kg-K}
> >   0.9000000    ,   !- Thermal Emittance
> >   0.5000000    ,   !- Solar Absorptance
> >   0.5000000    ;   !- Visible Absorptance
> >
> >
> >
> > But i didnt get the properties of polyurethane 4 in . How can i
> > manage the properties of Polyurethane 4 in ?
> >
> > And the Galv steel is 1/16 in ( 1.58 mm ). so how can i get the
> > values of Galv.steel which is 0.5 mm ?
> >
> > And what is the procedure of getting the properties of the material
> > which is not listed in the BLASTMaterials.idf file ?
> >
> > Could anybody help me in this regard .
> >
> > thank you
> >
> > khizir mahmud
> >
> >
> >
> >
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "chillarrahul"
> > <chillar@u...> wrote:
> > > Hi
> > > you will find the standard properties of your materials in the
> > > DataSet Folder where EnergyPlus is installed, when you reach data
> > > sets open up BLASTMaterials.idf   in notepad and search for your
> > > materials , you will find the required properties of various
> > > materials in the dataset folder.
> > >
> > > Thanks
> > >
> > > Rahul  Chillar
> > > Grad Research Assistant, Building Systems Lab
> > > Mechanical Engineering , University of Illinois - UC
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Khizir Mahmud
> > > <khizir_mahmud@y...> wrote:
> > > > Hi All
> > > >
> > > > In material-regular catagory i am working with two objects.
> > > >
> > > > 1. 0.5 mm galv. steel sheet
> > > > 2. Insulated Polyurethane (125 mm)
> > > >
> > > > Is there any energyplus recommended material guideline ? Or is
> > > there any standard source from where we could collect the value
>of
> > > the material properties. Could anyone help me in this regard.
> > > >
> > > > Thank you
> > > >
> > > > Khizir Mahmud
> > > >
> > > >
> > > >
>_________________________________________________________________
> > > >
> > > > Khizir Mahmud
> > > >
> > > > e-mail:    khizir_mahmud@y...
> > > >            khizir_mahmud@h...
> > > >
> > > >
> > > >
>_________________________________________________________________
> > > >
> > > > ---------------------------------
> > > > Do you Yahoo!?
> > > > Vote for the stars of Yahoo!'s next ad campaign!
> > > >
> > > > [Non-text portions of this message have been removed]
>
>
>
>The primary EnergyPlus web site is found at:
><<http://www.energyplus.gov>http://www.energyplus.gov> 
>http://www.energyplus.gov
>
>The group web site is:
><<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/> 
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate 
>folder in the Files area of the Support Web Site.
>
>
>
>
>
>
>Yahoo! Groups Sponsor
>
>
>ADVERTISEMENT
><<http://us.ard.yahoo.com/SIG=129ga1qm3/M=295196.4901138.6071305.3001176/D=groups/S=1705007389:HM/EXP=1090335337/A=2128215/R=0/SIG=10se96mf6/*http://companion.yahoo.com>http://us.ard.yahoo.com/SIG=129ga1qm3/M=295196.4901138.6071305.3001176/D=groups/S=1705007389:HM/EXP=1090335337/A=2128215/R=0/SIG=10se96mf6/*http://companion.yahoo.com> 
>click here
>
> 
><<http://us.adserver.yahoo.com/l?M=295196.4901138.6071305.3001176/D=groups/S=:HM/A=2128215/rand=165737939>http://us.adserver.yahoo.com/l?M=295196.4901138.6071305.3001176/D=groups/S=:HM/A=2128215/rand=165737939> 
>
>
>   _____
>
>Yahoo! Groups Links
>*         To visit your group on the web, go to:
><<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/> 
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>*         To unsubscribe from this group, send an email to:
><mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe> 
>EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
>*         Your use of Yahoo! Groups is subject to 
>the 
><<http://docs.yahoo.com/info/terms/>http://docs.yahoo.com/info/terms/> 
>Yahoo! Terms of Service.
>
>
>[Non-text portions of this message have been removed]
>
>
>
>The primary EnergyPlus web site is found at:
><http://www.energyplus.gov>http://www.energyplus.gov
>
>The group web site is:
><http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate 
>folder in the Files area of the Support Web Site.
>
>
>
>Yahoo! Groups Sponsor
>ADVERTISEMENT
><http://us.ard.yahoo.com/SIG=12910gcjd/M=295196.4901138.6071305.3001176/D=groups/S=1705007389:HM/EXP=1090337535/A=2128215/R=0/SIG=10se96mf6/*http://companion.yahoo.com>77ca4ec.jpg
>77ca514.jpg
>
>
>----------
>Yahoo! Groups Links
>    * To visit your group on the web, go to:
>    * 
> <http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/ 
>
>    *
>    * To unsubscribe from this group, send an email to:
>    * 
> <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx 
>
>    *
>    * Your use of Yahoo! Groups is subject to the 
> <http://docs.yahoo.com/info/terms/>Yahoo! Terms of Service.

Rahul  Chillar
Grad Research Assistant, Building Systems Lab
Mechanical Engineering , University of Illinois - UC
1206 West Green Street        217- 2441346 office
Urbana, IL 61801 USA            217-7213063 mobile
http://www.bso.uiuc.edu/~chillar/




[Non-text portions of this message have been removed]



------------------------ Yahoo! Groups Sponsor --------------------~--> 
Yahoo! Domains - Claim yours for only $14.70
http://us.click.yahoo.com/Z1wmxD/DREIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/