Re: [EnergyPlus_Support] question about Energy Recovery Ventilator: Stand Alone



I have determined that you can add a fan to your heat exchanger.  You 
will need to define a branch with the fan (and you will need another fan 
object) and include that branch in the branch list.  It appeared to work 
when I tested this configuration.

  BRANCH LIST,
    Air Loop Branches,       !- Branch List Name
    Air Loop Main Branch,    !- Branch Name 1
    Exhaust Branch;

  BRANCH,
    Exhaust Branch,
    1.3, ! your mass flow rate
    FAN:Simple:VariableVolume,  !- Comp3 Type
    Supply Fan 2, !- Comp3 Name
    Heat Recovery Secondary Outlet Node,  !- Comp3 Inlet Node Name
    Exhaust Node, !- Comp3 Outlet Node Name
    ACTIVE; !- Comp3 Branch Control Type
 


Richard Raustad wrote:

> The Stand Alone ERV is modeled as a piece of zone equipment and should
> only be used with other zone equipment objects.  Stand alone actually
> refers to the fact that it is not connected to an air loop.  For
> instance, if you have a window AC unit (zone equipment) conditioning a
> single zone you can also have a stand alone ERV connected to that zone. 
> This model can not be used with unitary equipment installed in an air
> loop if the zone the stand alone ERV serves is connected to the
> thermostat zone controlling the air loop equipment. You should be able
> to connect it to any other zone connected to that air loop (except the
> thermostat zone).  If you do this you will have to adjust (increase) the
> supply air flow rate to this zone to pick up the additional load
> contributed by the ERV.  If your modeling a school and the air loop does
> not condition the gymnasium, then you can attach a stand alone ERV to
> the gymnasium.
>
> If all zones are connected to an air loop then use the Heat
> Exchanger:Air to Air object connected to the air loop (e.g. supply side
> of the heat exchanger in the air loop; exhaust side inlet node of the
> heat exchanger connected to the relief air node of the outside air
> system and exhausted to outdoors) to perform the energy recovery.  After
> reading you other email message (shown below for reference), I believe
> you are trying to simulate this configuration.  You can not include an
> exhaust fan if you connect the exhaust side of the heat exchanger to the
> outside air mixer relief node.  The flow rate of the relief node is set
> by the outdoor air mixer object, not a fan.
>
> You may try connecting all zone exhausts to a mixer and passing that air
> stream through a fan and then through the exhaust side of the heat
> exchanger.  You will probably be the first person to try this and I
> would be interested to know how it turns out.
>
> Good Luck.
>
> Other email message:
> I am modeling a single zone building with a unitary
> system:blowthrough:heatcool. I have a air-air heat recovery to
> recover the heat from the exhaust air. I have built a supply fan in
> the unitary system. In addition, I want to have an exhaust fan. I am
> not sure whether I can implement that in EnergyPlus or not.
>
>
> zhaicq98 wrote:
>
> > Hi,
> >
> > I am not so sure that I understand the component ERV:stand alone. Can
> > it be used together with other equipment such as unitary equipment?
> > Does "stand alone" mean this is the only HVAC component for a zone?
> >
> > Thanks.
> >
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
> > appropriate folder in the Files area of the Support Web Site.
> >
> >
> >
> > Yahoo! Groups Sponsor
> > ADVERTISEMENT
> > 
> <http://us.ard.yahoo.com/SIG=129o20f17/M=295196.4901138.6071305.3001176/D=groups/S=1705007389:HM/EXP=1090602415/A=2128215/R=0/SIG=10se96mf6/*http://companion.yahoo.com> 
>
> >
> >
> >
> > ------------------------------------------------------------------------
> > Yahoo! Groups Links
> >
> >     * To visit your group on the web, go to:
> >       http://groups.yahoo.com/group/EnergyPlus_Support/
> >       
> >     * To unsubscribe from this group, send an email to:
> >       EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> >       
> <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>
> >       
> >     * Your use of Yahoo! Groups is subject to the Yahoo! Terms of
> >       Service <http://docs.yahoo.com/info/terms/>.
> >
> >
>
> -- 
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL  32922-5703
> Phone:   (321) 638-1454
> Fax:     (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>
>
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the 
> appropriate folder in the Files area of the Support Web Site.
>
>
>
> Yahoo! Groups Sponsor
> ADVERTISEMENT
> <http://us.ard.yahoo.com/SIG=129bdppur/M=295196.4901138.6071305.3001176/D=groups/S=1705007389:HM/EXP=1090609631/A=2128215/R=0/SIG=10se96mf6/*http://companion.yahoo.com> 
>
>
>
> ------------------------------------------------------------------------
> Yahoo! Groups Links
>
>     * To visit your group on the web, go to:
>       http://groups.yahoo.com/group/EnergyPlus_Support/
>        
>     * To unsubscribe from this group, send an email to:
>       EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>       <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>
>        
>     * Your use of Yahoo! Groups is subject to the Yahoo! Terms of
>       Service <http://docs.yahoo.com/info/terms/>.
>
>

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



[Non-text portions of this message have been removed]



------------------------ Yahoo! Groups Sponsor --------------------~--> 
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/