[EnergyPlus_Support] Re: ** Fatal ** Air Primary Loop VAV SYS 1 has no air flow
Thanks Mike,
Actually I had autosized everything, but the problem apparently had
its start when I commented out one of my DesignDay statements in
order to get the simulation to run a bit faster.
Because of the straightforwardness of this part of the input file, I
didn't read the documentation. The E+ programmers might want to
issue a warning if something seems amiss.
Shaun
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@g...> wrote:
> My apologies for the delayed response.
>
> This indicates that the air loop has been sized to zero flow.
First, check
> your AIR PRIMARY LOOP object. Is the "Primary air design
volumetric flow rate"
> field set to zero? It must have a value >0 or be set to Autosize.
If that is
> not the problem, then check the autosizing reports in the eio
file. Are the
> zone air flow rates being sized to zero? If so, there may be
something wrong
> with the sizing objects or the thermostat controls.
>
> Mike
>
>
> On 15 Jul 2004, at 19:51, sm278424 wrote:
>
> > Hi, another question/problem, I know this has something to do
with
> > nodes/branches but I can't seem to spot it.
> > Any ideas as to where I should look?
> > Thanks
> > Shaun
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
appropriate folder
> > in the Files area of the Support Web Site.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
> >
>
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@g...
------------------------ Yahoo! Groups Sponsor --------------------~-->
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/