Re: [EnergyPlus_Support] Re: Exceeding maximum iterations problem
There appears to be a bug affecting this run which combines a VAV system, zone
exhaust fans, and a return fan. Eliminating the zone exhaust fans fixes the
problem. It might also work to eliminate the return fan.
Mike
On 12 Jul 2004, at 21:39, bsiengineer wrote:
> Zheng,
>
> Thank you for your response.
>
> My model has only two zones. I have previously run this model many
> times with a constant volume system, and encountered no errors.
>
> I have manipulated the convergence tolerances with no effect on the
> iterations.
>
> My model has no economizer, so the outside temperature limit will not
> affect it. I think that in many US buildings the value of 19 is a
> good choice. The best temperature limit for a dry-bulb economizer
> depends on the typical outdoor conditions and the typical return air
> conditions. If your return air is 25 C and is normally more humid
> than the outdoor air then 25 may be a good choice, but I think this
> would be very unusual.
>
> Regards, David
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, zhen tian <tianzhen9@y...>
> wrote:
> > I had this iteration problem tried this method before.
> >
> > I found this problem was related to the zone number and zone
> equipment. The more zones, and the more equipement in the same zone,
> the more possibilty of this iteration problem.
> >
> > I found that if you set the convege tolerance to 0.00005, and this
> still appear, even you set minor values, this method will not work.
> >
> > Try to change the ousiside temperature limit from 19 to 20 or 18,
> this warning may go away. The example file uses 19 degree C, but I do
> not think it is correct. It should be around 24 to 26. You can give
> me a response if it works.
> >
> > From my perepective view, it will be better for the uses if
> Energyplus can focus on solve and improve the prolems in the existing
> models rather than to incorporate new models right now.
> >
> > By the way, I want to ask if somebody or some company has succeedly
> used Energyplus for simulating of real big building projects.
> >
> > Regards, Zhen
> >
> > bsiengineer <arch_engel@h...> wrote:
> > Rahul,
> >
> > Thank you for your help. I have made several simulation runs with
> > different convergence tolerances (both increased and decreased
> > values) on the cooling coil controller and reheat controllers but
> > these changes have had no effect on the number of iterations
> reported
> > in the error file. Does anybody have any other suggestions?
> >
> > Thanks, David
> >
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Rahul Chillar
> > <chillarrahul@y...> wrote:
> > > Hello
> > > This same problem had occured with a user earlier , ...........
> Max
> > > Iteration errors can be eliminated by increasing the convergence
> > tolerance
> > > on your controllers
> > >
> > > For example look at the controller information below and you will
> > easily figure out how to solve that. If it does not kindly let us
> > know so that we can look at your file which you uploaded.
> > >
> > > EARLIER CASE with problems:
> > >
> > > CONTROLLER:SIMPLE,
> > > Central Cooling Coil Contoller 1, !- Name
> > > TEMP, !- Control variable
> > > Reverse, !- Action
> > > FLOW, !- Actuator variable
> > > VAV Sys 1 Outlet Node, !- Control_Node
> > > Cooling Coil Water In, !- Actuator_Node
> > > 0.002, !- Controller Convergence Tolerance: delta
> > > temp from setpoint temp {deltaC}
> > > autosize, !- Max Actuated Flow {m3/s}
> > > 0.0000001; !- Min Actuated Flow {m3/s}
> > >
> > >
> > > CONTROLLER:SIMPLE,
> > > Central Heating Coil Contoller 1, !- Name
> > > TEMP, !- Control variable
> > > Normal, !- Action
> > > FLOW, !- Actuator variable
> > > VAV Sys 1 Outlet Node, !- Control_Node
> > > Main Heating Coil 1 Water Inlet Node, !- Actuator_Node
> > > 0.002, !- Controller Convergence Tolerance: delta
> > > temp from setpoint temp {deltaC}
> > > autosize, !- Max Actuated Flow {m3/s}
> > > 0.0000001; !- Min Actuated Flow {m3/s}
> > >
> > > These values created over 350 Max Iteration warnings. Then the
> > values were
> > > changed to:
> > > CONTROLLER:SIMPLE,
> > > Central Cooling Coil Contoller 1, !- Name
> > > TEMP, !- Control variable
> > > Reverse, !- Action
> > > FLOW, !- Actuator variable
> > > VAV Sys 1 Outlet Node, !- Control_Node
> > > Cooling Coil Water In, !- Actuator_Node
> > > 0.001, !- Controller Convergence Tolerance: delta
> > > temp from setpoint temp {deltaC}
> > > autosize, !- Max Actuated Flow {m3/s}
> > > 0.0000001; !- Min Actuated Flow {m3/s}
> > >
> > >
> > > CONTROLLER:SIMPLE,
> > > Central Heating Coil Contoller 1, !- Name
> > > TEMP, !- Control variable
> > > Normal, !- Action
> > > FLOW, !- Actuator variable
> > > VAV Sys 1 Outlet Node, !- Control_Node
> > > Main Heating Coil 1 Water Inlet Node, !- Actuator_Node
> > > 0.001, !- Controller Convergence Tolerance: delta
> > > temp from setpoint temp {deltaC}
> > > autosize, !- Max Actuated Flow {m3/s}
> > > 0.0000001; !- Min Actuated Flow {m3/s}
> > >
> > > The errors were reduced to over 50 Max iteration warnings.
> > >
> > > When Values Changed to
> > > CONTROLLER:SIMPLE,
> > > Central Cooling Coil Contoller 1, !- Name
> > > TEMP, !- Control variable
> > > Reverse, !- Action
> > > FLOW, !- Actuator variable
> > > VAV Sys 1 Outlet Node, !- Control_Node
> > > Cooling Coil Water In, !- Actuator_Node
> > > 0.0001, !- Controller Convergence Tolerance: delta
> > > temp from setpoint temp {deltaC}
> > > autosize, !- Max Actuated Flow {m3/s}
> > > 0.0; !- Min Actuated Flow {m3/s}
> > >
> > >
> > > CONTROLLER:SIMPLE,
> > > Central Heating Coil Contoller 1, !- Name
> > > TEMP, !- Control variable
> > > Normal, !- Action
> > > FLOW, !- Actuator variable
> > > VAV Sys 1 Outlet Node, !- Control_Node
> > > Main Heating Coil 1 Water Inlet Node, !- Actuator_Node
> > > 0.0001, !- Controller Convergence Tolerance: delta
> > > temp from setpoint temp {deltaC}
> > > autosize, !- Max Actuated Flow {m3/s}
> > > 0.0; !- Min Actuated Flow {m3/s}
> > >
> > >
> > > ALL MAX ITERATION ERROR ELIMINATED.
> > > Try the same procedure in your file , i am sure they will go
> away.
> > These occur because outer loop has higher tolerance set than inner
> > loop . Hence it is unable to converge.
> > > If they go away with above change you need not worry about the
> > results even if you loosen up the tolerance.
> > >
> > > Thanks
> > > Rahul Chillar
> > > Graduate Research Assistant
> > > Building Systems Laboratory
> > > Univerisity of Illinois UC
> > >
> > >
> > >
> > >
> > > bsiengineer <arch_engel@h...> wrote:
> > > My simulation is having a problem of exceeding the maximum
> > iterations
> > > on the HVAC system. I am simulating two interior rooms served by
> a
> > > single-duct VAV reheat system. This model has previously been
> run
> > > successfully with a single-duct constant volume system. The
> system
> > > is electric preheat and reheat, and purchased chilled water
> > cooling,
> > > so it's fairly simple.
> > >
> > > I will upload my file, Iterations.idf, to the
> > > folder "Problem_Submittals". Can anyone help me figure out what
> is
> > > going wrong?
> > >
> > > Thanks!
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
Yahoo! Domains - Claim yours for only $14.70
http://us.click.yahoo.com/Z1wmxD/DREIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/