The COMIS model only calculates infiltration and mixing flow rates, it has no
impact on the window solar calculations. So, you are correct, that the window
solar gain is modeled as if the windows are closed at all times.
Mike
On 18 Aug 2004, at 11:42, leeslwong wrote:
> Hi,
>
> I simulated a case that a room has 2 windows (one is facing to east
> and the other is facing to west). Using the COMIS method, the window
> are scheduled to open all the time. After the simulation, the air
> flow rates are normal and acceptable. But when I am looking at the
> window/zone transmitted solar, the result is adnormal because it is
> assumed the windows are still there (close). It is what I think. Is
> it the windows are still be closed when calculating transmitted solar
> and the windows are opened when calculating the COMIS ventilation at
> the same time? Or I am wrong?
>
> Thanks
>
> lee
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/