Re: [EnergyPlus_Support] total cooling load
Hello
To determine the actual latent loads you will have to simulate an hvac system, i think purchased air will give only the sensible total loads and not latent because it is not a system which can control the humdity levels etc of your zones.
Purchased air is designed as a wonderful concept to get the user in the ball park without having to simulate a system.
Reporting the below variables should be sufficent for your case where you only need to heat the building.
HVAC,Average,Purchased Air Total Cooling Rate[W]
HVAC,Sum,Purchased Air Total Cooling Energy[J]
thanks
Rahul Chillar
teklay Weldeabzgi <teklay1979@xxxxxxxxx> wrote:
i am simulating buildings to know the cooling load
reduction using different building design parameters.
i am using a purchased air system. we i need to see
the total cooling energy of the zones is the
AIR:Purchased Air Total Cooling Energy give me the
result. the ONE:Zone/Sys Sensible Cooling Energy gives
the sensible energy only. is AIR:Purchased Air Total
Cooling Energy the sum of the latent heat gain and the
sensible heat gain. to make cealr my question how do i
get the cooling load of the building?
tek
__________________________________
Do you Yahoo!?
New and Improved Yahoo! Mail - Send 10MB messages!
http://promotions.yahoo.com/new_mail
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups SponsorADVERTISEMENT
---------------------------------
Yahoo! Groups Links
To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.
Thanks
Rahul Chillar
Grad Student
Building Systems lab
Univ Of Illinois Urbana Champaign
---------------------------------
Do you Yahoo!?
New and Improved Yahoo! Mail - Send 10MB messages!
[Non-text portions of this message have been removed]
------------------------ Yahoo! Groups Sponsor --------------------~-->
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/