Re: [EnergyPlus_Support] Radiant Slab Outside Environment



When the outside environment is set to OtherZoneSurface, EnergyPlus forces the 
outside surface temperature to equal the inside surface temperature of the 
specified OtherZoneSurface.  Making the surface containing the cooling system 
adiabatic will only be valid if the construction of that surface is symmetrical 
and the cooling source is in the center of the construction.  

Is there a radiant cooling slab in between all of the floors?  If so, you can 
set the exterior environment of the 2nd level floor to be the 2nd level 
ceiling, and set the exterior enviorment of the 2nd level ceiling to be the 2nd 
level floor.  This creates a situation where two surfaces in the same zone are 
connected as interzone surfaces.  If the situation truly repeats itself, this 
can be a valid approach.

Mike


On 19 Aug 2004, at 12:15, zhen tian wrote:

> Hi:
> 
> I am simulating a multi-floor building with radiant slab cooling system.  The
> radiant floor is between two floors.  But I only want to simulate one floor. 
> For example, the radiant slab is between 2 and 3 floor.  I only want to simlate
> the 2th floor.  So how can simulate the 2th floor without simulating the 3rd
> floor?  Since the radiant floor will have effect on the 3rd floor and the 3rd
> fllor is conditioned too. Can I define the foor as adiabatic surface?  Or how
> can I define the outside environment for the slab surface?
> 
> Thanks a lot.
> 
> Regards,
> 
> Zhen
> 
> 
> ---------------------------------
> Do you Yahoo!?
> New and Improved Yahoo! Mail - Send 10MB messages!
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




------------------------ Yahoo! Groups Sponsor --------------------~--> 
$9.95 domain names from Yahoo!. Register anything.
http://us.click.yahoo.com/J8kdrA/y20IAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/