[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Re: design load output questions
Ahh, very helpful, thank you.
P317 of the I/O reference talks about the sizing issue - I had
specified the Design Flow Rate for the air system, so the program
calculates a sizing factor.
Your answer leads to two more questions:
1. In this case, can I assume that the loss to the back side of the
radiant panel is: (4161.89 + 8105.6) - 11587.44 = 680.05 ? This
would be to a plenum, in this instance.
2. Is there a way to get a handle on the peak latent load for the
zone and the air system aside from 'Zone,Sum,Zone-Total Internal
Latent Gain[J]'?
Thanks again
Shaun Martin
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@g...> wrote:
> I am guessing that you have a zone which is served by both an air
system and a
> radiant hydronic system.
>
> 1. The sizing reported in the zsz file is before application of
the sizing
> factor, the eio sizing includes the sizing factor. If this is no
1.0 (in
> either SIZING PARAMETERS or ZONE SIZING), then the values will not
be the same.
>
> 2. No. None of the values shown below include latent cooling,
they are all
> sensible loads. Values a and b are simulation results, values c
and d are
> sizing results. With radiant systems, unlike air systems, not all
of the
> cooling input to the slab will end up in the space. Values c and d
are zone
> cooling requirements which are completely independent of the type
of system
> which will serve the zone. Value a is the cooling energy input to
the radiant
> system, and some will be lost out the back side of the surface.
>
> Mike
>
>
> On 20 Aug 2004, at 15:52, sm278424 wrote:
>
> > Hi
> >
> > I wonder if someone can help me interpret some of the E+ output.
I'm
> > trying to do some design sizing. From one run, I have:
> >
> >
> > a) file.CSV - Z1 RADIANT PANEL:Hydronic Low Temp Radiant Cooling
Rate
> > [W](Hourly) = 4161.89 W (autosized)
> >
> > b) file.CSV - ZN1:E PERIM SPC:Zone/Sys Sensible Cooling Rate[W]
> > (Hourly) = 8105.6 (fixed 6 ACH)
> >
> > c) file.EIO - DesLoad {W} Cooling = 10277.00 W
> >
> > d) file.ZSZ - ZN1:E PERIM SPC:VANC_INTL CLG .4% DB=>MWB:Des Cool
> > Load [W] = 11587.44 W
> >
> >
> > my two questions are:
> >
> > 1. should c and d be the same? or, why not?
> >
> > 2. should (a + b + latent) = c or d?
> >
> > Thanks
> >
> > Shaun Martin
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
appropriate folder
> > in the Files area of the Support Web Site.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
> >
>
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@g...
------------------------ Yahoo! Groups Sponsor --------------------~-->
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/