Re: [EnergyPlus_Support] space cooling load calculation for each contributor?
EnergyPlus does not report component loads, because the heat balance is done as
a combined solution and the presence of one load can affect the impact of
another load. The best way to determine this breakdown is to run multiple
simulations, first with just the envelope, then a run adding infiltration, then
add ventilation, and so on until all components are present in the run. If you
change the order in which you add components, you may get slightly different
answers for the incremental component loads.
Mike
On 27 Aug 2004, at 12:06, Zheng Li wrote:
> Dear all:
>
> I want to calculate the space cooling load for a residential building with a
> window type air conditioner. The T and RH setpoint are 24¢J, 50%, respectively.
> The cooling load contributors include envelope, ventilation, infiltration,
> people, light, electric equipment and internal mass(furniture et al.). Can I use
> the EnergyPlus to get the space total, sensible and latent cooling load for each
> contributor, specially the latent one? Or the EnergyPlus can only get the A/C
> system cooling load and sensible load for all the contributors?
>
> Thanks!
>
> Best Regards
> LI
>
>
> ---------------------------------
> Á§³ÍµXÁn¦â¹Ï®×¡B»yµ²á¤Ñ¡B¼eÀWWebcamµ¥¦h¶µ¥\¯à
> ¥þ·s Yahoo! Messenger
> http://messenger.yahoo.com.hk
>
> [Non-text portions of this message have been removed]
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/