Here is the formula:

    ! Calculate Sky IR
    !HIR = ESKY * SIGMA * (TOUT**4)
    !
    !where
    !
    !HIR = horizontal IR intensity (W/m2)
    !ESKY = sky emissivity
    !SIGMA = Stefan-Boltzmann constant = 5.6697e-8 W/m2-K4
    !TOUT = drybulb temperature (K)
    !
    !The sky emissivity is given by
    !
    !ESKY = [0.787 + 0.764*ln(TDEW/273)]*[1 + 0.0224*N - 0.0035*(N**2) +
0.00028*(N**3)]
    !
    !where
    !
    !TDEW = dewpoint temperature (K)
    !N = opaque sky cover (tenths)
    !
    !Example: Clear sky (N=0), TOUT = 273+20=293K, TDEW = 273+10=283K:
    !
    !ESKY = 0.787 + 0.764*0.036 = 0.815
    !HIR = 0.815*5.6697e-8*(293**4) = 340.6 W/m^2

    !References:
    !
    !George N. Walton, "Thermal Analysis Research Program Reference Manual,"
    !NBSIR 83-2655, March 1983, p. 21.
    !
    !G. Clark and C. Allen, "The Estimation of Atmospheric Radiation for
Clear and
    !Cloudy Skies," Proc. 2nd National Passive Solar Conference (AS/ISES),
1978, pp. 675-678.

I suppose the manual should be changed to just say "opaque sky cover".



Linda

EnergyPlus WebSite: http://www.energyplus.gov
Owner: EnergyPlus_Support list
Member: EnergyPlus Development Team



[Non-text portions of this message have been removed]



------------------------ Yahoo! Groups Sponsor --------------------~-->
$9.95 domain names from Yahoo!. Register anything.
http://us.click.yahoo.com/J8kdrA/y20IAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/