Re: [EnergyPlus_Support] Nominal supply air flow rate
An air-to-air heat exchanger is typically used for pretreating outdoor
air. The "Nominal supply air flow rate" should be within the range of
50% to 130% of the outdoor air flow rate. The nominal supply air flow
rate specifies the rating point for the air-to-air heat exchanger and is
not necessarily the actual operating flow rate. The actual air flow
rate can be higher or lower than the nominal air flow rate as long as it
is within 50% to 130% of the nominal supply air flow rate. If the
outdoor air flow rate is autosized and the user attempts to specify the
flow rate through the air-to-air heat exchanger, the specified flow rate
must be in the range of 50% to 130% of the autosized outdoor air flow
rate. If a specific outdoor air flow rate is required for the
air-to-air heat exchanger for a given simulation, do not autosize the
outdoor air flow rate. If autosizing the outdoor air flow rate is
desired, run the simulation and check the *.eio file for the autosized
outdoor air flow rate and set the "Nominal supply air flow rate" through
the heat exchanger to be within 50% to 130% of this value. See Heat
Exchanger:Air to Air:Generic in the Engineering document for further
details.
pizzaalan wrote:
> Dear all,
>
> How can I determine "Nominal supply air flow rate" in Heat
> Exchanger:Air to Air Generic. I know it should be the minimum flow
> rate, but it is autosized by the program. When I give an
> unreasonable number, a bunch of warnings comes out.
>
> Thanks.
>
> Alan
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files area of the Support Web Site.
>
>
>
> Yahoo! Groups Sponsor
> ADVERTISEMENT
> <http://us.ard.yahoo.com/SIG=129f2f7sa/M=295196.4901138.6071305.3001176/D=groups/S=1705007389:HM/EXP=1095503153/A=2128215/R=0/SIG=10se96mf6/*http://companion.yahoo.com>
>
>
>
> ------------------------------------------------------------------------
> Yahoo! Groups Links
>
> * To visit your group on the web, go to:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> * To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>
>
> * Your use of Yahoo! Groups is subject to the Yahoo! Terms of
> Service <http://docs.yahoo.com/info/terms/>.
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
[Non-text portions of this message have been removed]
------------------------ Yahoo! Groups Sponsor --------------------~-->
$9.95 domain names from Yahoo!. Register anything.
http://us.click.yahoo.com/J8kdrA/y20IAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/