Re: [EnergyPlus_Support] COMIS and PA




The key point is that the COMIS simulation calculates airflows for infiltration 
and zone-to-zone mixing without any knowledge of HVAC system flows.  You can 
use COMIS to ventilate and use PURCHASED AIR to calculate the heating/cooling 
loads.

Mike


On 1 Oct 2004, at 14:50, alexandrevarela2000 wrote:

> Hello all,
> 
> I read that COMIS has some problems regarding HVAC systems (COMMIS 
> Cannot Do - page 299). Is PA (purchased air) included in these "HVAC 
> systems"?
> 
> I want to ventilate (open windows...) and calculate the energy needs 
> to meet the room load, so I´m using PA and COMIS. Is this ok?
> 
> On the other hand I want to know the infiltration rate for the room, 
> due to open windows. In order to do this I have to use PA with NO 
> OUTSIDE AIR, right?
> 
> I´m having these doubts because I thought PA was an "ideal" system 
> working as an energy needs "calculator", and now I see that maybe I 
> was wrong.
> 
> Have a nice weekend!
> Alexandre
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




------------------------ Yahoo! Groups Sponsor --------------------~--> 
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/