Re: [EnergyPlus_Support] Heating:Electricity



I am assuming this is the same input file that we were looking at last month 
(2e3102.imf).  This mode is a VAV system serving 16 zones with hot water reheat 
coils served by an electric boiler.  The VAV "Zone Minimum Air Flow Fraction" 
fields are all set to either 0.3 or 0.5, and the reheat coils and boiler are 
scheduled to be on at all times the fan system operates.  So, whenever a zone 
sees a cooling load below 30% (or 50%) of the peak design cooling load, the 
reheat coil will come on to prevent overcooling.

Mike


On 3 Oct 2004, at 5:57, beyangj wrote:

> 
> 
> Dear,
> 
> The building in my IDF file is located in Hong Kong, but the 
> simulation results showed  that the Heating:Electricity was needed 
> all the year round.Especially, the amount of Heating:Electricity in 
> January was 1.08E+11 J, but that in July was 1.55E+10 J. In summer, 
> the temperature in Hong Kong is very high, so there should be no 
> need for heating. I don't know why this happened. Could you kindly 
> help me?
> 
> Best,
> 
> Stewart
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




------------------------ Yahoo! Groups Sponsor --------------------~--> 
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/