I upload the input file to the file area for further analysis. I am
using V1.2.1. I did not simulate the latent load degradation
phenomanon.
Thanks!
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Chaoqin Zhai
<chaoqinz@a...> wrote:
> Yes, I checked the temperature as well. The indoor temperature is
around
> 23oC, which is my setpoint. The temperature of the air coming from
the
> cooling coil is around 12 oC. There is sensible cooling on the
coil, but
> very little latent cooling.
>
> Thanks,
> Chaoqin
>
> --On Wednesday, October 27, 2004 2:38 PM +0000 donbshireyiii
> <shirey@f...> wrote:
>
> >
> > Are you sure that the DX cooling coil is operating during the time
> > when you are seeing these conditions?
> >
> > From what you describe, it seems like you are mixing about 40-50%
> > outdoor air with 50-60% return air from the zone, and this air is
> > being supplied back to the zone (with the cooling coil OFF). Did
you
> > check the temperatures as well?
> >
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "zhaicq98"
<chaoqinz@a...>
> > wrote:
> >>
> >> Hi,
> >>
> >> I have a unitary system with DX cooling coil to condition a
> > one-zone
> >> building. I output the supply air condition as well as the indoor
> > and
> >> outdoor air condition and I found something strange. The supply
air
> >> humidity ratio is around 7 g/kg dry air, but the indoor humidity
> >> ratio is around 5 g/kg. At that period the outdoor humidity ratio
> > is
> >> around 9-10 g/kg. I have some occupants inside the zone. I do not
> >> have infiltration when the HVAC is working. It seems so confusing
> > to
> >> me and I would greatly appreciate it if someone can give me some
> >> hints on it.
> >>
> >> Thanks a lot!
> >
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
appropriate
> > folder in the Files area of the Support Web Site.
> >
> >
> >
> > Yahoo! Groups Sponsor
> > ADVERTISEMENT
> > [Image: "click"]
> > [Image: "width=1"]
> >
> > __________________________________________________
> > Yahoo! Groups Links
> >
> > * To visit your group on the web, go to:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > * To unsubscribe from this group, send an email to:
> > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> >
> > * Your use of Yahoo! Groups is subject to the Yahoo! Terms of
Service.
------------------------ Yahoo! Groups Sponsor --------------------~-->
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/