Use the error messages to guide you to the problem. The error messages refer
to specific object and node names to pinpoint the problem.
1. For example, the first warning:
** Warning ** Node used as an inlet more than once: COOLING COIL WATER INLET
NODE-FCUZONEGF7
Search the idf file for this node name, and it will become evident that two
different branches (CCOILBRANCH-FCUZONEGF9 and CCOILBRANCH-FCUZONEGF7) refer to
the same cooling coil. The inputs for CCOILBRANCH-FCUZONEGF9 are in error.
2. Next there are some thermostat object errors reported.
3. The remaining node connection errors are probably false errors as noted in
the err file: ** Warning ** Node Connection errors shown during "fatal
error" processing may be false because not all inputs may have been retrieved.
Ignore these until the problems in 1 and 2 have been fixed.
Mike
On 30 Oct 2004, at 19:23, wing sun lee wrote:
>
> Hi,
>
> It is so terrible for me to find that errors in the input file and in the
> branch/node details file.
>
> Would you mind helping me find the errors of these connection node. I have
> already double checked for a few days, but failed.
>
> Please help!! I am very glad to hear your good news.
>
> Regards,
>
> SAMLEE
>
> Encl.
>
>
> ɹL¡B¤@©ç¨â´²¡B©_¬¥§õºû´µ¦^«H...
> ¥þ´ä³Ì¤j¤â¾÷¤U¸ü¤¤¤ß
> http://mobile.yahoo.com.hk/
>
>
> [Non-text portions of this message have been removed]
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
$9.95 domain names from Yahoo!. Register anything.
http://us.click.yahoo.com/J8kdrA/y20IAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/