Re: [EnergyPlus_Support] Temperature out of range on a High rise with plenums




These anomalies are happening at very low load conditions in "Detailed Flat 
Cooling Coil 1".  If you change the Min Actuated Flow in the controller for 
this coil from 0.0000001 to zero, the errors go away with a negligible change 
in results.

Also, I noticed that the schedule specified for PEOPLE activity level is a 
fractional schedule (0 to 1).  This schedule is in W/person, so the internal 
heat gain from PEOPLE is way too low.

Mike


On 1 Nov 2004, at 18:20, herma015 wrote:

> 
> 
> This error occurs several times on my high rise.  The idf is about 1 
> meg so I'm having trouble posting it.  
> 
> This is a design day run and the ventilation system starts at 6:00 
> am so it must be some type of heat balance problem.  The 
> temperatures shown in the error msg below are really screwy. 
> 
> How can I get the idf file to you?
> 
>  ** Warning ** Temperature out of range [-100. to 200.] 
> (PsyPsatFnTemp)
>    **   ~~~   **  Occurrence info=MPLS/STPAUL SUMMER, 07/21 06:15 - 
> 06:30
>    **   ~~~   **  Input Temperature=28423.76
>    ** Warning ** Calculated Humidity Ratio is invalid (PsyWFnTdbRhPb)
>    **   ~~~   **  Occurrence info=MPLS/STPAUL SUMMER, 07/21 06:15 - 
> 06:30
>    **   ~~~   **  Dry-Bulb= 28423.76 Relative Humidity (fraction)= 
> 1.00 Pressure= 98300.00
>    **   ~~~   ** Calculated Humidity Ratio= -0.6639 ... Humidity 
> Ratio set to .00001
>    ** Warning ** Temperature out of range [-100. to 200.] 
> (PsyPsatFnTemp)
>    **   ~~~   **  Occurrence info=MPLS/STPAUL SUMMER, 07/21 06:15 - 
> 06:30
>    **   ~~~   **  Input Temperature=49612.21
>    ** Warning ** Calculated Humidity Ratio is invalid (PsyWFnTdbRhPb)
>    **   ~~~   **  Occurrence info=MPLS/STPAUL SUMMER, 07/21 06:15 - 
> 06:30
>    **   ~~~   **  Dry-Bulb= 49612.21 Relative Humidity (fraction)= 
> 1.00 Pressure= 98300.00
>    **   ~~~   ** Calculated Humidity Ratio= -0.6639 ... Humidity 
> Ratio set to .00001
>    ** Warning ** Temperature out of range [-100. to 200.] 
> (PsyPsatFnTemp)
>    **   ~~~   **  Occurrence info=MPLS/STPAUL SUMMER, 07/21 06:15 - 
> 06:16
>    **   ~~~   **  Input Temperature=36686.55
>    ** Warning ** Calculated Humidity Ratio is invalid (PsyWFnTdbRhPb)
>    **   ~~~   **  Occurrence info=MPLS/STPAUL SUMMER, 07/21 06:15 - 
> 06:16
>    **   ~~~   **  Dry-Bulb= 36686.55 Relative Humidity (fraction)= 
> 1.00 Pressure= 98300.00
>    **   ~~~   ** Calculated Humidity Ratio= -0.6639 ... Humidity 
> Ratio set to .00001
>    ** Warning ** Temperature out of range [-100. to 200.] 
> (PsyPsatFnTemp)
>    **   ~~~   **  Occurrence info=MPLS/STPAUL SUMMER, 07/21 06:15 - 
> 06:16
>    **   ~~~   **  Input Temperature=49591.79
>    ** Warning ** Calculated Humidity Ratio is invalid (PsyWFnTdbRhPb)
>    **   ~~~   **  Occurrence info=MPLS/STPAUL SUMMER, 07/21 06:15 - 
> 06:16
>    **   ~~~   **  Dry-Bulb= 49591.79 Relative Humidity (fraction)= 
> 1.00 Pressure= 98300.00
>    **   ~~~   ** Calculated Humidity Ratio= -0.6639 ... Humidity 
> Ratio set to .00001
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




------------------------ Yahoo! Groups Sponsor --------------------~--> 
$9.95 domain names from Yahoo!. Register anything.
http://us.click.yahoo.com/J8kdrA/y20IAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/