[EnergyPlus_Support] Re: question about air-air heat recovery with economizer
Chaoqin:
You are correct. Selecting ECONOMIZER or BYPASS should have worked.
I ran your input data file. You see only 1 error message, at the very
beginning of the simulation (Jan 1 at 00:10).
It turns out that there is a faulty initialization being performed in
the air-to-air heat exchanger model during the "warm up" calculations
at the beginning of the simulation.
Disregard the error message; this initialization issue should have
virtually no impact on your results. We'll fix it for the next
release.
Don
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Chaoqin Zhai
<chaoqinz@a...> wrote:
> As I read from the IO reference, both ECONOMIZER and BYPASS could
be
> specified together with the air-air total heat recovery. The
difference is
> that by specifying BYPASS the outside air flow rate remain the
minimum
> value whether it passes the HX or not.
>
> -Chaoqin
>
> --On Thursday, November 04, 2004 3:41 PM -0500 Richard Raustad
> <RRaustad@F...> wrote:
>
> > Economizer choice for Controller:Outside Air should be set to
"Bypass"
> > when heat recovery is used. See Heat Exchanger:Air To
Air:Generic in
> > the IO Reference Manual for further details.
> >
> > Chaoqin Zhai wrote:
> >
> >> Hi,
> >>
> >> I have an air-air total heat recovery in the system. In
addition, I
> >> set the
> >> system could go into economizer mode when the outdoor condition
is
> >> within a
> >> certain limit. When I ran the simulation using EnergyPlus, an
error
> >> message
> >> is generated, which said: HEAT EXCHANGER:AIR TO AIR:GENERIC "ERV"
average
> >> air volume flow rate is <50% or >130% of the nominal HX supply
air volume
> >> flow rate.
> >>
> >> To my understanding it is because the outside air flow rate is
getting
> >> higher than the minimum outside air flow rate, which is the same
as
> >> nominal
> >> air flow rate of the ERV, when the system is in economizer mode.
Am I
> >> right? Will this warning affect the calculation accuracy of the
> >> simulation?
> >>
> >> Thanks a lot!
------------------------ Yahoo! Groups Sponsor --------------------~-->
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/