Re: [EnergyPlus_Support] question about air-air heat recovery with economizer
As I read from the IO reference, both ECONOMIZER and BYPASS could be
specified together with the air-air total heat recovery. The difference is
that by specifying BYPASS the outside air flow rate remain the minimum
value whether it passes the HX or not.
-Chaoqin
--On Thursday, November 04, 2004 3:41 PM -0500 Richard Raustad
<RRaustad@xxxxxxxxxxxx> wrote:
> Economizer choice for Controller:Outside Air should be set to "Bypass"
> when heat recovery is used. See Heat Exchanger:Air To Air:Generic in
> the IO Reference Manual for further details.
>
> Chaoqin Zhai wrote:
>
>> Hi,
>>
>> I have an air-air total heat recovery in the system. In addition, I
>> set the
>> system could go into economizer mode when the outdoor condition is
>> within a
>> certain limit. When I ran the simulation using EnergyPlus, an error
>> message
>> is generated, which said: HEAT EXCHANGER:AIR TO AIR:GENERIC "ERV" average
>> air volume flow rate is <50% or >130% of the nominal HX supply air volume
>> flow rate.
>>
>> To my understanding it is because the outside air flow rate is getting
>> higher than the minimum outside air flow rate, which is the same as
>> nominal
>> air flow rate of the ERV, when the system is in economizer mode. Am I
>> right? Will this warning affect the calculation accuracy of the
>> simulation?
>>
>> Thanks a lot!
>>
>>
>> The primary EnergyPlus web site is found at:
>> http://www.energyplus.gov
>>
>> The group web site is:
>> http://groups.yahoo.com/group/EnergyPlus_Support/
>>
>> Attachments are not allowed -- please post any files to the
>> appropriate folder in the Files area of the Support Web Site.
>>
>>
>>
>> Yahoo! Groups Sponsor
>> ADVERTISEMENT
>> <http://us.ard.yahoo.com/SIG=12920g2vj/M=315388.5543473.6613715.3001176/
>> D=groups/S=1705007389:HM/EXP=1099683876/A=2372354/R=0/SIG=12id813k2/*htt
>> ps://www.orchardbank.com/hcs/hcsapplication?pf=PLApply&media=EMYHNL40F21
>> 004SS>
>>
>>
>>
>> ------------------------------------------------------------------------
>> Yahoo! Groups Links
>>
>> * To visit your group on the web, go to:
>> http://groups.yahoo.com/group/EnergyPlus_Support/
>>
>> * To unsubscribe from this group, send an email to:
>> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>> <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Uns
>> ubscribe>
>>
>> * Your use of Yahoo! Groups is subject to the Yahoo! Terms of
>> Service <http://docs.yahoo.com/info/terms/>.
>>
>>
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>
>
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate
> folder in the Files area of the Support Web Site.
>
>
>
> Yahoo! Groups Sponsor
> ADVERTISEMENT
> [Image: "click"]
> [Image: "width=1"]
>
> __________________________________________________
> Yahoo! Groups Links
>
> * To visit your group on the web, go to:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> * To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> * Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.
------------------------ Yahoo! Groups Sponsor --------------------~-->
$9.95 domain names from Yahoo!. Register anything.
http://us.click.yahoo.com/J8kdrA/y20IAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/