The "Day Type" affects all schedules (people, lights, equipment, fans, 
thermostat setpoints).  My guess is that the thermostat control type is set to 
cooling only for "SummerDesignDay".  Change the heating design day daytype to 
"WinterDesignDay".

Mike


On 10 Nov 2004, at 4:20, beyangj wrote:

> 
> 
> Dear, 
> 
> In my IDF file, I defined two DesignDays, namely summer design day 
> and winter design day.  The summer design day object had field Day 
> Type set to SummerDesignDay, and the winter design day object had 
> field Day Type set to SummerDesignDay. The winter design day was Jan 
> 21 1989 first, but the system didn¡¯t work on this design day 
> simulation, there was no heating and no cooling on that day. Then I 
> set the winter design day as Jan 20 1989,   but that didn¡¯t work 
> yet. I wondered why that happened, and that would affect the results 
> of  heating energy?
> 
> best,
> 
> Stewart
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




------------------------ Yahoo! Groups Sponsor --------------------~--> 
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/