Re: [EnergyPlus_Support] about the minimum system air flow ratio




You may not have a simulation mistake.  A variable air volume system
will use heat during summer cooling to avoid over cooling a space.  For
instance, if your system discharges 50F air, but the cooling load only
requires 60F air at the minimum flow volume, heat will be needed to
maintain set point temperature.  Typically you will need a cold supply
air temperature to lower the dew point of the ventilation air for
humidity control.  Maintaining humidity control requires heating to
avoid over cooling the space.

Ned Lyon

Senior Project Manager
Simpson Gumpertz & Heger Inc.

41 Seyon Street
Building #1, Suite 500
Waltham, MA  02453

Phone:  781-907-9000
Fax:  781-907-9009


>>> beyangj@xxxxxxxxxxx 11/11/2004 10:03:09 AM >>>

Dear,
In my simulation, the minimum system air flow ratio and the zone 
minimum air flow fraction were varied several times, and that 
affected the result of cooling energy slightly, but that affected 
the result of heating energy obviously.  I am wondering why there is 
some heating in the summer days, and the heating just occurs in the 
period the system is turned on. When the ratio and the fraction 
mentioned before are set smaller, the heating in the summer would 
also become smaller. As a matter of fact, there is no heating in the 
summer days, but there is always some heating in the summer days 
even the minimum system air flow ratio is set as 0.01. How can I get 
rid of this mistake? In addition,  I want to know how much these 
ratio values  affect the results. Thanks in advance!

Best,

Stewart






The primary EnergyPlus web site is found at:
http://www.energyplus.gov 

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/ 

Attachments are not allowed -- please post any files to the appropriate
folder in the Files area of the Support Web Site.



Yahoo! Groups SponsorADVERTISEMENT

Yahoo! Groups Links
To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/ 
  To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx 
  Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.




------------------------ Yahoo! Groups Sponsor --------------------~--> 
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/