Re: [EnergyPlus_Support] Air primary loop has no air flow?????




In the <Zone Sizing Information> report in the eio output file, all of the zone 
design loads are zero.  This usually indicates a problem with the thermostat 
inputs.  The Zone_control_type_day schedule is incorrect.  It it always 0.044, 
which is interpreted as zero which means no heating or cooling is active.  This 
schedule should only contain integer values from 0 to 4.  See the section about 
Zone Control:Thermostatic in the Input Output Reference (p. 659, pdf p. 689) 
for an explanation of the thermostat control type schedule.  

Mike

On 29 Nov 2004, at 2:38, hbn_pch wrote:

> 
> 
> Hi,
>   i just simulate a story buinding.But it tells me that the air 
> primary loop has no air flow???Why???
>   Is the loop connection false???I've uploaded my idf.
> 
>   Thanks for all your kind help!!!!! 
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




------------------------ Yahoo! Groups Sponsor --------------------~--> 
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/