[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Re: Air primary loop has no air flow?????





Hi,
  Thank you very much,Mike.According to your hint,i modify the 
example and the previous problem is cleared away.However,it appear 
new warnings,which are all the same:

** Warning ** Error -- Mass Flow Rate Calculation in Plant 
Loop=HEATING LOOP, Outlet and Inlet differ by more than tolerance.
   **   ~~~   ** Loop inlet node=HP INLET, 
flowrate=1.142157060549204E-002
   **   ~~~   ** Loop outlet node=PS_H_OP_OUTLET, 
flowrate=2.284314121098408E-002

** Warning ** Error -- Mass Flow Rate Calculation in Plant 
Loop=HEATING LOOP -- continues ** 500
   ** Warning ** Error -- Mass Flow Rate Calculation in Plant 
Loop=HEATING LOOP -- continues ** 1000
   ** Warning ** Error -- Mass Flow Rate Calculation in Plant 
Loop=COOLING LOOP -- continues ** 1500
   ** Warning ** Error -- Mass Flow Rate Calculation in Plant 
Loop=COOLING LOOP -- continues ** 2000
   ** Warning ** Error -- Mass Flow Rate Calculation in Plant 
Loop=COOLING LOOP -- continues ** 2500

** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC 
loops, at SUMMER DESIGN, 07/21 08:36 - 08:37
   ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC 
loops, at SUMMER DESIGN, 07/21 08:37 - 08:38

  Expect your kind reply,thanks!



--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte" 
<mjwitte@g...> wrote:
> In the <Zone Sizing Information> report in the eio output file, all 
of the zone 
> design loads are zero.  This usually indicates a problem with the 
thermostat 
> inputs.  The Zone_control_type_day schedule is incorrect.  It it 
always 0.044, 
> which is interpreted as zero which means no heating or cooling is 
active.  This 
> schedule should only contain integer values from 0 to 4.  See the 
section about 
> Zone Control:Thermostatic in the Input Output Reference (p. 659, 
pdf p. 689) 
> for an explanation of the thermostat control type schedule.  
> 
> Mike
> 
> On 29 Nov 2004, at 2:38, hbn_pch wrote:
> 
> > 
> > 
> > Hi,
> >   i just simulate a story buinding.But it tells me that the air 
> > primary loop has no air flow???Why???
> >   Is the loop connection false???I've uploaded my idf.
> > 
> >   Thanks for all your kind help!!!!! 
> > 
> > 
> > 
> > 
> > 
> > 
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> > 
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> > 
> > Attachments are not allowed -- please post any files to the 
appropriate folder
> > in the Files area of the Support Web Site.
> > 
> > Yahoo! Groups Links
> > 
> > 
> > 
> > 
> > 
> > 
> > 
> > 
> > 
> 
> 
> 
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support      
> EnergyPlus-Support@g...





------------------------ Yahoo! Groups Sponsor --------------------~--> 
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/