Re: [EnergyPlus_Support] temperature
For the building envelope, only GroundTemperatures is used. The other ground
temperatures (deep, surface, etc.) are used for ground contact HVAC equipment.
The ground temperature should vary month by month. Custom ground temperatures
can be calculated using the Slab program provided with EnergyPlus. See the
Auxiliary Programs document for instructions.
Mike
On 30 Nov 2004, at 12:55, ozgur gocer wrote:
>
> Dear all,
> I'm a newie to E+. I have start from input output references to learn e+. I have
> questions. In ground temperature(deep, surface etc) we enter same value for all
> months. And there are some default temperatures. (13, 16 Centigrate etc.) 1-But
> if we use Istanbul weather data what will the constant temperature for ground
> temperature? 2- or can i enter different temperature values for each month?
>
> P.S: Is e+ appropriate for atrium building simulation? If somebody have tried to
> simulate atriums, i need more knowledge please contact me. Thanks reading it.
>
>
>
> ---------------------------------
> Do you Yahoo!?
> Yahoo! Mail - Helps protect you from nasty viruses.
>
> [Non-text portions of this message have been removed]
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
$9.95 domain names from Yahoo!. Register anything.
http://us.click.yahoo.com/J8kdrA/y20IAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/