1. Zone13 is cooking (over 100C).  This is the source of the psychrometric 
errors.

2.  Some walls are slightly cooler than the outdoor dry bulb at night.  This is 
normal.  The sky temperature is approximately -25C at those times.

3.  Zone13 and Zone16 have adiabatic floors.  This is why they are warmer than 
similar zones.

4.  The ground temperatures are too extreme.  The entered values look more like 
undisturbed (open field) ground temperatures.  The ground under a conditioned 
building is usually more in the range of 2-3C cooler than the inside 
temperature.  Use the slab program, or use 18C as a default.  See the Auxiliary 
Progams document for instructions for the Slab program.

5.  To add temperature controls, add ZONE CONTROL:THERMOSTATIC, PURCHASED AIR, 
and related objects.  See PurchAir.idf example file.


On 8 Dec 2004, at 9:44, ping sun wrote:

> 
> hi,
>    I have upload my idf file,please hlpe me to check it thank you !
>    I simulate a six stories building.In order to find the fault easily,I
>    simulate the first story. In the result that the temperature of the outside
>    surface is lower than Outdoor Dry Bulb,or higher than 90¡æ.I can not find the
>    reason!
>   please help me thank you!
> 
> 
> 
> ---------------------------------
> Do You Yahoo!?
> ×¢²áÊÀ½çÒ»Á÷Æ·ÖʵÄÑÅ»¢Ãâ·ÑµçÓÊ
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




------------------------ Yahoo! Groups Sponsor --------------------~--> 
$4.98 domain names from Yahoo!. Register anything.
http://us.click.yahoo.com/Q7_YsB/neXJAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/