[EnergyPlus_Support] Re: comis : windows vertices
Thanks Mike.
Andrea.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@g...> wrote:
> We are still investigating the surface overlap errors. While
experimenting
> with the input, I stumbled across a change that eliminates the
COMIS errors.
> Move the first vertex on "Zn002: ap alta ovest" to be the last
vertex. This
> changes the first vertex from the uppermost to the leftmost:
>
> Surface:HeatTransfer:Sub,
> Zn002: ap alta ovest, !- User Supplied Surface Name
> <snip>
> 9.9, !- Vertex 2 X-coordinate {m}
> 24.8769, !- Vertex 2 Y-coordinate {m}
> 7.7404, !- Vertex 2 Z-coordinate {m}
> 9.9, !- Vertex 3 X-coordinate {m}
> 15.1609, !- Vertex 3 Y-coordinate {m}
> 2.9005, !- Vertex 3 Z-coordinate {m}
> 9.9,
> 15.1163,
> 2.99,
> 9.9, !- Vertex 1 X-coordinate {m}
> 24.8324, !- Vertex 1 Y-coordinate {m}
> 7.8299; !- Vertex 1 Z-coordinate {m}
>
> As we learn more, we will let you know. Much of the EnergyPlus
team is on
> vacation/holiday this week, so it will probably be after the New
Year before we
> know more.
>
> Mike
>
>
> On 23 Dec 2004, at 8:44, ingdallolio wrote:
>
> >
> >
> > Thanks Linda,
> > The version I used to run the case is the December 2004 one, but
I
> > wrote the imput file with the previous one.
> > I did write the openin vertices CCW direction but, I think,
because
> > of the fact the opening sides are not vertical and horizontal E+
do
> > not "see" I'm going CCW ?? is that possible ?
> > I have now included in report all the air flow rates, all the
> > openings have allways positive flow rates, what does that means ?
> > I uploaded the file.
> > Grazie.
> > Andrea.
> >
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Linda Lawrie
<linda@l...>
> > wrote:
> > > The "Base does not surround subsurface" is coming from the main
> > EnergyPlus
> > > and not because they are COMIS openings. This usually means
you
> > have
> > > overlapped the window with the base surface OR possibly that
you
> > have the
> > > incorrect starting corner or direction (CW vs CCW) in
specifying
> > the
> > > surface or window vertices.
> > >
> > > I'm not sure what the COMIS Error is -- there should be some
> > accompanying
> > > message to say what it is complaining about.
> > > >>If I use 3 vertices windows still COMIS complain but do not
make
> > > >>reference to those openings I just get :
> > > >>AN ERROR IS REPORTED (Comis) ventilation OUTPUT IS LIKELY TO
BE
> > WRONG
> > >
> > > Which EnergyPlus version are you using?
> > >
> > > You may wish to upload your input file or send it to us for
further
> > detection.
> > >
> > > At 02:42 AM 12/22/2004, ingdallolio wrote:
> > > >My walls upper rentilation openings on the est and west walls
are
> > > >parallel to the roof slope, if I keep the openings
rectangular
> > COMIS
> > > >do not like that I get an error message:
> > >
> > > Linda
> > >
> > > EnergyPlus WebSite: http://www.energyplus.gov
> > > Owner: EnergyPlus_Support list
> > > Member: EnergyPlus Development Team
> > >
> > >
> > >
> > > [Non-text portions of this message have been removed]
> >
> >
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
appropriate folder
> > in the Files area of the Support Web Site.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
> >
> >
> >
> >
------------------------ Yahoo! Groups Sponsor --------------------~-->
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/