Re: [EnergyPlus_Support] Re: comis : windows vertices



We are still investigating the surface overlap errors.  While experimenting 
with the input, I stumbled across a change that eliminates the COMIS errors.  
Move the first vertex on "Zn002: ap alta ovest" to be the last vertex.  This 
changes the first vertex from the uppermost to the leftmost:

Surface:HeatTransfer:Sub,
    Zn002: ap alta ovest,    !- User Supplied Surface Name
<snip>
    9.9,                     !- Vertex 2 X-coordinate {m}
    24.8769,                 !- Vertex 2 Y-coordinate {m}
    7.7404,                  !- Vertex 2 Z-coordinate {m}
    9.9,                     !- Vertex 3 X-coordinate {m}
    15.1609,                 !- Vertex 3 Y-coordinate {m}
    2.9005,                  !- Vertex 3 Z-coordinate {m}
    9.9,
    15.1163,
    2.99,
    9.9,                     !- Vertex 1 X-coordinate {m}
    24.8324,                 !- Vertex 1 Y-coordinate {m}
    7.8299;                  !- Vertex 1 Z-coordinate {m}

As we learn more, we will let you know.  Much of the EnergyPlus team is on 
vacation/holiday this week, so it will probably be after the New Year before we 
know more.

Mike


On 23 Dec 2004, at 8:44, ingdallolio wrote:

> 
> 
> Thanks Linda,
> The version I used to run the case is the December 2004 one, but I 
> wrote the imput file with the previous one.
> I did write the openin vertices CCW direction but, I think, because 
> of the fact the opening sides are not vertical and horizontal E+ do 
> not "see" I'm going CCW ?? is that possible ?
> I have now included in report all the air flow rates, all the 
> openings have allways positive flow rates, what does that means ?
> I uploaded the file.
> Grazie.
> Andrea.  
> 
> 
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Linda Lawrie <linda@l...> 
> wrote:
> > The "Base does not surround subsurface" is coming from the main 
> EnergyPlus 
> > and not because they are COMIS openings.  This usually means you 
> have 
> > overlapped the window with the base surface OR possibly that you 
> have the 
> > incorrect starting corner or direction (CW vs CCW) in specifying 
> the 
> > surface or window vertices.
> > 
> > I'm not sure what the COMIS Error is -- there should be some 
> accompanying 
> > message to say what it is complaining about.
> > >>If I use 3 vertices windows still COMIS complain but do not make
> > >>reference to those openings I just get :
> > >>AN ERROR IS REPORTED (Comis)  ventilation OUTPUT IS LIKELY TO BE 
> WRONG
> > 
> > Which EnergyPlus version are you using?
> > 
> > You may wish to upload your input file or send it to us for further 
> detection.
> > 
> > At 02:42 AM 12/22/2004, ingdallolio wrote:
> > >My walls upper rentilation openings on the est and west walls are
> > >parallel to the roof slope, if I keep the openings rectangular  
> COMIS
> > >do not like that I get an error message:
> > 
> > Linda
> > 
> > EnergyPlus WebSite: http://www.energyplus.gov
> > Owner: EnergyPlus_Support list
> > Member: EnergyPlus Development Team
> > 
> > 
> > 
> > [Non-text portions of this message have been removed]
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 






------------------------ Yahoo! Groups Sponsor --------------------~--> 
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/