I am not sure exactly what you are asking. First, you need a set of
performance data for the chiller which gives capacity and power consumption
over a range of condenser and chilled water temperatures and a range of part
loads. Then, the data is manipulated and curve-fit for each of the various
curves. Most users develop a spreadsheet to take the available data and
produce curve-fit coefficients.
On 7 Jan 2005, at 9:35, samwslee wrote:
>
>
> Dear sir,
>
> Would you mind giving some advice to get the coefficient of power
> ratio curve and full load ratio curve for chiller.
>
> Regards,
>
> SAMLEE
>
>
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/