Re: [EnergyPlus_Support] Loop delta Temp




Loop delta T is only used when autosizing the plant loop flow rate.  See the 
PLANT SIZING object in 5ZoneAuto.idf  

Mike


On 20 Jan 2005, at 11:56, zhen tian wrote:

> 
> Hi, Mike:
> 
> As you suggested, I checked the model "VAVSingleDuctReheatBaseboard.idf".
> 
> But I found that the temperature of 6.67C is set for the chilled water supply
> temperature, not the loop DeltaT. Am I right? 
> 
> Could you tell me where can I set the chilled water and hot water loop DeltaT? I
> guess I can set these DeltaT in the field of Plant Loop by setting Maximum and
> Minimum loop temperature.  But I found that in examples, these DeltaT is quite
> big. For chilled water loop, it is ranged from 1degree C to 98 degree C. Can I
> set a reasonable Delta T in this filed?
> 
> Thanks a lot.
> 
> Regards,
> 
> Zhen
> 
> "Michael J. Witte" <mjwitte@xxxxxxxx> wrote:
> The temperature rise across the loop will depend on how you have sized the flow
> rate vs. load in the coils.  Many (all?) of the example files use a 6.67C loop
> DeltaT.
> 
> Mike
> 
> 
> On 17 Jan 2005, at 17:17, zhen tian wrote:
> 
> > 
> > Hi, Mike:
> > 
> > I changed the Pump cofficeints to "0, 1, 0, 0" and now the "HW PUMP OUTLET
> > NODE:System Node Temp[C](Hourly) " and the "CW PUMP OUTLET NODE:System Node
> > Temp[C](Hourly) " are kept at 93 degree C and 5C, and accords well to the set
> > temperatures. 
> > 
> > But I checked the CW SUPPLY INLET NODE TEMP and CW PUMP OULET NODE TEMP, I
> > still get some temperatures like these: "5, 5, 5.5, 10.9, 15.4..." which are
> > close to the set temperatures, are these temperatures sound normal? 
> > 
> > Thanks a lot.
> > 
> > Regards,
> > 
> > Zhen
> > 
> > 
> > 
> > "Michael J. Witte" <mjwitte@xxxxxxxx> wrote:
> > If the pump power remains constant and the flow varies, low flows will get hot
> > because the energy must go somewhere.  You either need to let the pump power
> > vary (linear power would use coefficients of 0,1,0,0) or use a constant speed
> > pump so the excess flow will go through the bypass.
> > 
> > Mike
> > 
> > On 14 Jan 2005, at 16:39, zhen tian wrote:
> > 
> > > 
> > > Hi, Mike:
> > > 
> > > Thanks for you reply. I have checked the pump input. Actually, I do use
> > > variable flow pumps with constant pump power.  But I cannot change rated
> > > pump power consumption to "autosize" as this will cause severe errors. I did
> > > not use any autosize function in my model.  I have upload my model named "
> > > ICT-NoRC-zt.zip " to the yahoo group. Could you check it for me? Thanks a
> > > lot. The weather file is Calgary, Alberta.
> > > 
> > > Regards,
> > > 
> > > Zhen 
> > 
> > 
> > ---------------------------------
> > Do you Yahoo!?
> >  Yahoo! Mail - 250MB free storage. Do more. Manage less.
> > 
> > [Non-text portions of this message have been removed]
> > 
> > 
> > 
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> > 
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> > 
> > Attachments are not allowed -- please post any files to the appropriate folder
> > in the Files area of the Support Web Site.
> > 
> > Yahoo! Groups Links
> > 
> > 
> > 
> > 
> > 
> > 
> > 
> > 
> > 
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> 
> 
> 
> ---------------------------------
> Yahoo! Groups Links
> 
>    To visit your group on the web, go to:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
>    To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> 
>    Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service. 
> 
> 
> __________________________________________________
> Do You Yahoo!?
> Tired of spam?  Yahoo! Mail has the best spam protection around 
> http://mail.yahoo.com 
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/