zhen tian wrote:

>Hi, All:
> 
>I have a question about using the heat exchanger object. I found that if I use "Heat Exchanger: air to air: flat plate" , I do not need a set point manager, but when I use "Heat Exchanger: air to air: Generic", it requires a set point manager for heat exchanger. Could somebody tell me why?
>  
>
The Heat Exchanger:Air To Air:Generic can modulate to control the supply 
air temperature to a set point which requires a set point manager but 
only when Supply Air Outlet Temperature Control is set to "Yes". If 
Supply Air Outlet Temperature Control is set to "No" a set point manager 
is not required. The flat plate heat exchanger can not control to a 
temperature set point and does not need a set point manager (modulation 
of heat recovery is not supported). It does, however, allow an 
economizer mode where free cooling is available when the outside air 
controller INCREASES the outdoor air flow rate above the flat plate heat 
exchangers design air flow rate. See the IO reference manual for further 
details of air to air heat exchangers.

> 
>By addding a heat exchanger, I found that the heating energy use decreased a lot but the cooling energy use increased much in winter.  I do use economizer within 20C to 4C outside temperature. I check the node temperature, when the heat recovery outlet node temperature can meet the setpoint (14C), but the mixed is about 17C to 20C and higher than supply air temperature 15.6C. This is the result of the mixture of some portion of return air. 
> 
>Is there any solution to control the mixed temperaure?  I use a set point manager for the mixed air temperature control. But sounds like if there was some portion of return air mixture, the mixed air temperature will be higher than supply air temp, when the outside temperature varies between -10C to 4C (winter).
> 
>Could sombody tell me how to avoid this situation?
>  
>
There is a trade off when using a heat exchanger for energy or heat 
recovery. As you describe the winter heating energy can be significantly 
reduced when energy is recovered. The cooling energy, however, can 
increase in winter when the economizer set points are set to low. The 
heat exchanger is active until the upper economizer limit is reached and 
pre-heats the incoming outdoor air which may require additional cooling 
to meet the desired set point. Increase the upper economizer limit (up 
to the return air temperature) and watch the cooling energy in winter 
decrease as the set point is moved upward. To optimize the simulation, 
select the economizer set points such that ANNUAL energy use is 
minimized and compare this annual energy use with the same simulation 
without an air to air heat exchanger. The economizer set points will 
vary based on geographic location, cooling and heating set points, 
internal loads, and building construction.

> 
>Thanks a lot for your help.
> 
>Regards,
> 
>Zhen
>
>		
>---------------------------------
>Do you Yahoo!?
> The all-new My Yahoo! – Get yours free!    
>
>[Non-text portions of this message have been removed]
>
>
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
> 
>Yahoo! Groups Links
>
>
>
> 
>
>
>
>
>  
>

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/