Re: [EnergyPlus_Support] Weather Data Problem



At 04:32 AM 2/1/2005, wong@xxxxxxxxxxxxxxxxxxxxxxxxx  wrote:
>I face a problem in weather data.
>I changed the values of a few parameters in the weather file
>JPN_Osaka_IWEC but find it could not run during simulation, with
>error message:
>
>unexpected error condition in the middle of reading EPW file, stopped
>at 1999/12/31 24:60

I believe you've erased some end of line markers.  One between 12/29/hr:15 
and 12/29/hr:16   and another where 1/24/hr22 is totally missing.  I will 
put a trap for future runs / releases in EnergyPlus for this.  EnergyPlus 
must have contiguous files, no missing hours of data.

You probably used a text editor to make your changes?  It would be safer to 
create a "csv" file using the weather converter, use Excel or other 
spreadsheet program to make your changes and then save it back to csv file 
to be re-read into the weather converter.  Sounds like a few too many steps 
but less likely to have the problems you're seeing.

Linda


[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/