Re: [EnergyPlus_Support] Input problem in chiller:electric
The six "design" values represent the chiller performance at one operating
point, usually the published rating point for the chiller. As the water
temperatures and part-load change, then the capacity and COP (1/EIR) will
change. To define your own performance curves, you will need the manufacturer
to provide a set of capacity and COP data for a range of condenser and chilled
water temperatures. If you do not have access to such data, then use one of
the sets of curves provided in \DataSets\PerfCurves.idf
Mike
On 3 Feb 2005, at 16:57, wing sun lee wrote:
>
> Hi,
>
> 1. For the Chiller:electric Object at the page no. 383 of InputOutputReference
> Doc., the capacity ratio curve.
>
> How to determine the value of "Ratio of Available Capacity to Nominal Capacity"?
> Is the value of nominal capacity getting from e.g. Carrier's catalogue, then how
> about the value of available capacity and its stand for?
>
> How to determine the value of "Temperature entering the condenser" and
> "Temperature leaving the evaporator"? Is these values comming from catalogue and
> what is the difference between these values with "TempCondInDesign" and
> "TempEvapOutDesign".
>
> Thanks,
>
> SAMLEE
>
>
>
> ɹL¡B¤@©ç¨â´²¡B©_¬¥§õºû´µ¦^«H...
> ¥þ´ä³Ì¤j¤â¾÷¤U¸ü¤¤¤ß
> http://mobile.yahoo.com.hk/
>
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/