[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Re: Problems in maintaining humidity control
Hello,
I've manually increased the flowrate in the `sizing' objects (or
specifically, in the zone sizing object). This has had the desired
effect over the humidity (and by association the setpoint node's
fluctuations have levelled out). Thanks very much.
I would like to ask a follow up question if I may; is there
something wrong in my input that didn't allow EnergyPlus to autosize
a larger volumetric flowrate to offset this problem before my manual
input?
Also, I am getting too much fresh air in the summer design day (I
would like a minimum intake but I seem to be getting maximum
intake). I have scheduled a minOA Sched in the OA controller,
however it does not seem to take effect here. The winter OA intake
works fine, does this flag anything in particular?
Kind regards
-Elmer
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@g...> wrote:
> When using humidity control on the central chilled water coil, the
controller
> changes the chilled water setpoint to provide the required
humidity ratio
> needed to meet the humidistat setpoint. The varying setpoint
values reflect
> the adjusted setpoints for humidity control. Given the low
numbers being seen,
> it appears that the airflow rates are not adequate to meet the
humidity loads?
>
> Mike
>
>
> On 18 Feb 2005, at 8:25, Elmer Morrissey wrote:
>
> >
> >
> > Hello all,
> >
> >
> >
> > I am wondering if anyone has any experience in modelling VAV
systems that
> > maintain strict control over temperature AND humidity in a zone.
> >
> >
> >
> > I am modelling an AHU that provides air to two interior zones in
an art gallery.
> > I cannot seem to force the system to maintain control over the
zones over a 24hr
> > period as required by the Art Gallery.
> >
> >
> >
> > One of my major problems that I have found is a floating
setpoint on my VAV
> > system outlet node. During the winter, the setpoint output on
the csv emulates
> > the idf input, however during the summer design day, the csv
output for the
> > setpoint value floats from ?57oC to 3oC. I cannot seem to locate
the source of
> > this error as I have no errors or warning. It is scheduled to a
set value of
> > 17.5oC during the summer and 16oC during the winter. I also have
trouble
> > stipulating the flow using the sizing objects, they seem to be
ignored but I am
> > guess this is due to an error elsewhere in the idf.
> >
> >
> >
> > I have uploaded the file to the yahoo page?
AHU3_AirLoop_PurchasedPlant_V1.idf
> >
> >
> >
> > I would appreciate anyone's experience or advice with this
matter.
> >
> >
> >
> > Kind regards
> >
> >
> >
> > -Elmer Morrissey
> >
> >
> > PhD Researcher, IRUSE, NUIC, Ireland.
> >
> > __________________________________________________
> > Do You Yahoo!?
> > Tired of spam? Yahoo! Mail has the best spam protection around
> > http://mail.yahoo.com
> >
> > [Non-text portions of this message have been removed]
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
appropriate folder
> > in the Files area of the Support Web Site.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
> >
> >
> >
> >
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/