Re: [EnergyPlus_Support] Problems in maintaining humidity control
When using humidity control on the central chilled water coil, the controller
changes the chilled water setpoint to provide the required humidity ratio
needed to meet the humidistat setpoint. The varying setpoint values reflect
the adjusted setpoints for humidity control. Given the low numbers being seen,
it appears that the airflow rates are not adequate to meet the humidity loads?
Mike
On 18 Feb 2005, at 8:25, Elmer Morrissey wrote:
>
>
> Hello all,
>
>
>
> I am wondering if anyone has any experience in modelling VAV systems that
> maintain strict control over temperature AND humidity in a zone.
>
>
>
> I am modelling an AHU that provides air to two interior zones in an art gallery.
> I cannot seem to force the system to maintain control over the zones over a 24hr
> period as required by the Art Gallery.
>
>
>
> One of my major problems that I have found is a floating setpoint on my VAV
> system outlet node. During the winter, the setpoint output on the csv emulates
> the idf input, however during the summer design day, the csv output for the
> setpoint value floats from ?57oC to 3oC. I cannot seem to locate the source of
> this error as I have no errors or warning. It is scheduled to a set value of
> 17.5oC during the summer and 16oC during the winter. I also have trouble
> stipulating the flow using the sizing objects, they seem to be ignored but I am
> guess this is due to an error elsewhere in the idf.
>
>
>
> I have uploaded the file to the yahoo page? AHU3_AirLoop_PurchasedPlant_V1.idf
>
>
>
> I would appreciate anyone?s experience or advice with this matter.
>
>
>
> Kind regards
>
>
>
> -Elmer Morrissey
>
>
> PhD Researcher, IRUSE, NUIC, Ireland.
>
> __________________________________________________
> Do You Yahoo!?
> Tired of spam? Yahoo! Mail has the best spam protection around
> http://mail.yahoo.com
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/