It means that the values entered for these fields in the CONTROLLER:OUTSIDE AIR 
object named "OA CONTROLLER" are not consistent.  If one or both of these 
values are autosized, check the eio output file to see the autosized value.  
This should help diagnose what input is causing the problem.

Mike


On 24 Feb 2005, at 5:48, oldgun_hbns wrote:

> 
> 
> Hi:everyone!
>    my model show error:
>    Severe  ** For CONTROLLER:OUTSIDE AIR: OA CONTROLLER
>    **   ~~~   **   maximum outside air flow rate < minimun outside 
> air flow rate
> 
>    who Tell me what cause the error? thanks 
> 
> 
> 
> 
> 