Re: [EnergyPlus_Support] Re: about the window air conditioner
And FurnaceDXAuto.idf is an autosized example of the same type of system.
On 24 Feb 2005, at 12:50, donbshireyiii wrote:
>
>
> The window air conditioner model in EnergyPlus is "cooling only". In
> the example file WindAC.idf, the window air conditioner
> is coupled with a hot water baseboard heating system.
>
> A packaged terminal heat pump model (providing both heating and
> cooling) is scheduled to be added to EnergyPlus by the Fall 2005
> release.
>
> EnergyPlus contains a model that can be used for residential
> heating/cooling, which involves an air distribution system (common in
> the U.S.). See object "Furnace:Blowthru:HeatCool" in the IO Reference
> and the Engineering Doc. An example file is also provided:
> FurnaceWithDXSystem.idf
>
> Don
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "beyangj" <beyangj@h...>
> wrote:
> >
> > Dear,
> > In my residential building mdel, I set the ZONE EQUIPMENT LIST
> > object, AIR CONDITIONER:WINDOW:CYCLING and
> > COIL:DX:CoolingBypassFactorEmpirical object as follow,
> >
> > ZONE EQUIPMENT LIST,
> > GAB1Equipment, !- Name
> > AIR CONDITIONER:WINDOW:CYCLING, !- KEY--Zone Equipment Type 1
> > GAB1WindAC, !- Type Name 1
> > 1, !- Cooling Priority
> > 1; !- Heating Priority
> >
> > AIR CONDITIONER:WINDOW:CYCLING,
> > GAB1WindAC, !- name of window AC unit
> > System Available Schedule-B1, !- availability schedule
> > autosize, !- maximum air flow rate {m3/s}
> > autosize, !- maximum outside air flow rate {m3/s}
> > GAB1WindACAirInletNode, !- air inlet node
> > GAB1WindACAirOutletNode, !- air outlet node
> > GAB1WindACOAInNode, !- outside air node
> > GAB1WindACExhNode, !- air relief node
> > GAB1WindACOAMixer, !- outside air mixer name
> > GAB1WindACFan, !- fan name
> > GAB1WindACDXCoil, !- DX cooling coil name
> > CycFanCycComp, !- operation mode
> > blow through, !- fan placement
> > 0.001, !- Cooling Convergence Tolerance
> > COIL:DX:CoolingBypassFactorEmpirical; !- Cooling coil type
> >
> > COIL:DX:CoolingBypassFactorEmpirical,
> > GAB1WindACDXCoil, !- Coil Name
> > System Available Schedule-B1, !- Availability Schedule
> > autosize, !- Rated Total Cooling Capacity
> (gross)
> > {W}
> > autosize, !- Rated SHR
> > 3.0, !- Rated COP
> > autosize, !- Rated Air Volume Flow Rate {m3/s}
> > GAB1WindACFanOutletNode, !- Coil Air Inlet Node
> > GAB1WindACAirOutletNode, !- Coil Air Outlet Node
> > WindACCoolCapFT, !- Total Cooling Capacity Modifier
> > Curve (function of temperature)
> > WindACCoolCapFFF, !- Total Cooling Capacity Modifier
> > Curve (function of flow fraction)
> > WindACEIRFT, !- Energy Input Ratio Modifier Curve
> > (function of temperature)
> > WindACEIRFFF, !- Energy Input Ratio Modifier Curve
> > (function of flow fraction)
> > WindACPLFFPLR, !- Part Load Fraction Correlation
> > (function of part load ratio)
> > CycFanCycComp; !- Supply Air Fan Operation Mode
> >
> > When the model was run, there was only cooling energy sumption got,
> > and there was no heating consumption got. The heating period was
> set
> > from Jan.1 to Feb.28. I wondered there is a window air conditioner
> > model like the Residential System(RESYS) in Doe-2.2. There is a
> > residential heating and cooling system with a heating coil plus a
> DX
> > cooling-only condensing unit in the EnerguPlus? If so, there is an
> > example for this kind of residential heating and cooling system?
> >
> > Best,
> >
> > Stewart
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/