Re: [EnergyPlus_Support] Interior Window ventilation
I am not sure that I understand the question. Are you using COMIS openings?
If so, venting schedules apply to the zone receiving the ventilation. So, the
exterior openings would be controlled by the vent schedule in the sunspace and
the interior openings would be controlled by the vent schedule in the interior
zone. However, I am not sure if COMIS can model vent controls on an interior
window.
If you are not using COMIS to model the ventilation flow, CROSS MIXING behaves
the same whether there is a window in the shared wall or not. The basic window
surface object (Surface:HeatTransfer:Sub) only models conduction heat transfer
and solar gains; other objects must be specified to add airflow through a
window.
Mike
On 1 Mar 2005, at 12:10, ogocer@xxxxxxxxxxxxxx wrote:
>
> Dear Mike,
> Thanks a lot for your interest. i want to ask you a question about window
> or doors between zones.
> In my simulation there was no openings on the common wall separetes simple
> zone and sunspace. But it is not practical. Because there is no visual or
> pyhsical connection between two zones. So in first step i choose not
> defining any openings on common wall.
> Question is:
> how can i define a different schedule for openings on common wall? for
> example for winter when ventilation schedule is "off" for outside openings
> i want a schedule "on" for interior opennings.Because in reality these
> openings are used for entering the other zone. is it possible to define
> any other schedule for that interior window/door?
> Thanks alot.
> O.Gocer
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/