[EnergyPlus_Support] Re: Non-Zone equipment and Boiler in series
I searched the input files and made sure there were no typos - i
think the error was that I was mixing demand-side components with
supply-side ones (I thought a boiler could be on the demand side as
well), and for some reason it didn't reconognize that as the error.
I never got an errors mentioning invalid equipment configurations -
just the node connections. And I went through and cut and pasted my
node names in their respective places to make sure they were typed
exactly the same.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@g...> wrote:
> The "unknown" node errors usually indicate a typo somewhere. The
component
> type, component name, inlet node and outlet node must match
exactly in both the
> BRANCH object and the compoment object. Search your input file
for the node
> names listed in the errors and it should lead you to where the
problem is.
>
> However, if I understand the description below, it sounds like
this simulation
> is mixing demand-side components (DOMESTIC HOT WATER and radiant
hydronic) with
> supply-side components (boiler). This will not work. Did this
generate any
> other error messages such as "invalid equipment type"?
>
> Mike
>
>
> On 8 Mar 2005, at 0:02, colotupper wrote:
>
> >
> >
> > I am trying to run the following setup, but am getting some node
> > connection errors:
> >
> > I have a large water heater on the plant side of a water loop.
This
> > water heater is fed by solar collectors and has no backup
heating
> > element in it.
> >
> > On the demand side of my water loop, I have a splitter that does
to
> > DHW and a radiant heatings zone. I would like to have a
separate
> > electric boiler for both the DHW and the radiant zone, so I put
> > these boilers in series on the same branch with the DHW and
Radiant
> > system, respectively.
> >
> > When I did this, I received node connection errors and the types
of
> > my some of those nodes are know unknown. Is there some reason
why
> > you can't connect an boiler in series with Non-Zone Equipment
like
> > DHW?
> >
> > Thank you!
> >
> > Kendra Tupper
> >
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
appropriate folder
> > in the Files area of the Support Web Site.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
> >
> >
> >
> >
>
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@g...
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/