Re: [EnergyPlus_Support] error!
If there are only a few of these errors (less than 10), then you can safely
ignore them. If there are many of these errors, the first thing to do is to
autosize the "Controller Convergence Tolerance" in all CONTROLLER:SIMPLE
objects.
Mike
On 25 Mar 2005, at 2:30, energypluser wrote:
>
>
> Dear all,
>
> When I simulate a electric chiller using the manufacture's
> data, there is a warning come out as follow:
> SimHVAC: Maximum iterations exceeded for all HVAC loops
>
> How to solve this problem?
> Thank you in advance
>
>
> charlie
>
>
>
>
>